SmartConnector Processor not showing in Web Portal

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • SmartConnector Processor not showing in Web Portal
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
Adam_Summers
Lt. Commander Adam_Summers Lt. Commander
Lt. Commander

Posted: ‎2016-07-20 07:51 AM

0 Likes
2
1586
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-20 07:51 AM

SmartConnector Processor not showing in Web Portal

I have a problem with a SmartConnector I've developed.

We are deploying to a clean environment with SmartConnector installed but the Web Portal will not show the processor for selection when trying to add a new processor.

I've enabled all logging levels but can't see anything in the log to assist either. Can anyone help?

Reply
  • All forum topics
  • Previous Topic

Accepted Solutions
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2016-07-20 08:09 AM

2 Likes
1
1504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-20 08:09 AM

While deploying your SmartConnector Extension assembly to a production installation is straightforward, it is sometimes easy to forget to also include any assemblies that you may have referenced in your code that SmartConnector doesn’t know about.  Because the Portal uses reflection to analyze assemblies when it looks for Processor sub-classes, those assemblies with missing dependencies can’t be loaded and thus won’t show in the Portal.  There would be a handled exception that is logged which indicates the missing reference. 

Verify that your Logging Filters allow Portal events to be written to the log.  Also verify that your Service Settings allow for a Logging Level which includes Errors. After that, retry adding your Processor and review the log files.  My guess is that you will see an error indicating a missing assembly.

See Answer In Context

Reply
Replies 2
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2016-07-20 08:09 AM

2 Likes
1
1505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-20 08:09 AM

While deploying your SmartConnector Extension assembly to a production installation is straightforward, it is sometimes easy to forget to also include any assemblies that you may have referenced in your code that SmartConnector doesn’t know about.  Because the Portal uses reflection to analyze assemblies when it looks for Processor sub-classes, those assemblies with missing dependencies can’t be loaded and thus won’t show in the Portal.  There would be a handled exception that is logged which indicates the missing reference. 

Verify that your Logging Filters allow Portal events to be written to the log.  Also verify that your Service Settings allow for a Logging Level which includes Errors. After that, retry adding your Processor and review the log files.  My guess is that you will see an error indicating a missing assembly.

Reply
Adam_Summers
Lt. Commander Adam_Summers Lt. Commander
Lt. Commander

Posted: ‎2016-07-21 01:20 AM

1 Like
0
1504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-21 01:20 AM

Thanks Mark, that got us going on the right track. The issue was not a missing assembly that the log file suggested, but a dependency of that 3rd party assembly we were referencing. Using Dependency Walker against the 3rd Party dll highlighted which other related dependencies we were missing.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore