SmartConnector EWS questions

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • SmartConnector EWS questions
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SmartConnector Forum
Start a Topic
bbradley_jaxcon
Lieutenant | EcoXpert Master bbradley_jaxcon Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-06-09 07:57 AM

0 Likes
7
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-09 07:57 AM

SmartConnector EWS questions

We have developed our own SmartConnector processor and we seem to be experiencing some weird quirks on the StruxureWare side of SmartConnector (SmartConnector version 2.4.23). Our application will poll values from a variety of 3rd party devices and make those values accessible via a web service. Our SmartConnector processor will then communicate with those web services and make the values accessible to StruxureWare via an EcoStruxure Web Service. If the processor detects a change of value on the StruxureWare side the SmartConnector processor will then issue a write web service request to the point and change the value in the 3rd party device.
 
We are experiencing two quirks right now. 
 
The first is some of the points have a state of “Uncertain” when we look at them in EWS Server within SmartConnector. This does not seem to be an issue when bringing in values, but what makes the state “Uncertain?”
 
EWS_Server.png
 
The second is some of the points that we bring into StruxureWare seem to get coming in with an error. The points worked when we initially brought them in, but now they seem to be giving us an InvalidID error. If we delete and re-host the point it has an error right away, but we do not see any issues in the hardware folder except the state is marked “Uncertain.”
 
ErrorErrorHardware ExploreHardware Explore
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2020-06-09 08:51 AM

0 Likes
6
1994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-09 08:51 AM

HI Brian,

 

I’ll see if I can help!

 

  • Why do your points have a state of uncertain?
    • Since it looks like this state is showing ‘Uncertain’, not just in EBO, but also in Smart Connector, I believe this is actually completely up to your Smart Connector processor. When the point is created, or updated, you have the ability to set the ‘State’ of the point. I am curious if there is any place where this is accidentally being set to ‘Uncertain’?
  • Why are some points showing an error, with an INVALID_ID in EBO?
    • This generally happens because the EWS is retrieving Invalid_Id errors from the EWS server, are you able to verify there is a point in your EWS Server with the ID
       

 

Also, in general, It might also help to turn logging on ‘Trace’ in Smart Connector and make sure the ‘Ews Serve’ logging filter is set to true? We might get some additional info from Smart Connector that can help to debug this issue.

 

Best Regards,

 

-Jeff

Reply
bbradley_jaxcon
Lieutenant | EcoXpert Master bbradley_jaxcon Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-06-10 05:33 AM

0 Likes
1
1987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-10 05:33 AM

  • Uncertain States
    •  I got with the developer of our SmartConnector program and they informed me that they are not setting the state property and the default state is "uncertain." So it makes sense that all our values are uncertain
  • Invalid ID
    • I checked verified that the path is the EWS service does match what is in the EWS Server
    • I've attached a snippet of the log file 

EWSServerEWSServerSWClient_Hosted_ItemsSWClient_Hosted_Items

Attachments
2020-06-10.log
Reply
bbradley_jaxcon
Lieutenant | EcoXpert Master bbradley_jaxcon Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-06-12 06:28 AM

0 Likes
0
1981
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-12 06:28 AM

As an additional test I added another EWS service in a ASP on the site (The first EWS was in the ES) and it doesn't seem to be having any issues ATM. I'm keeping an eye on it.

Reply
bbradley_jaxcon
Lieutenant | EcoXpert Master bbradley_jaxcon Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-06-15 05:56 AM

0 Likes
3
1977
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-15 05:56 AM

Have you had a chance to look over the log yet? 

Reply
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2020-06-15 06:06 AM

0 Likes
2
1975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-15 06:06 AM

Hi!

 

Your logs look normal as far as I can see.. You mention that you tried creating the interface in an AS and it works as expected..

Did you delete and re-create the interface in the ES? Does the same thing happen? I am wondering if you can use SOAP UI (installed on the same machine as the ES), and try and send some requests to the EWS Server hosted in Smart Connector, and see what the response is.

 

If you need help with SOAP UI, please feel free to send me an email.

 

Best Regards,

 

-Jeff

Reply
bbradley_jaxcon
Lieutenant | EcoXpert Master bbradley_jaxcon Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-06-15 06:39 AM

0 Likes
0
1973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-15 06:39 AM

Yes everything is still working well in the ASP. We have some trends and binds setup with the points in the ES. I'll get with the guy who is setting up everything at the customer site on Wednesday when he returns and recreate the service. I'll let you know how everything goes.

Reply
bbradley_jaxcon
Lieutenant | EcoXpert Master bbradley_jaxcon Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-06-19 05:24 AM

0 Likes
0
1965
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-19 05:24 AM

I had the guy working on the site make an export of all the items in the ESWService. I then haphazard deleted about 75% items and the all the remaining hosted items started working again. After that I deleted the rest of the hosted objects and the EWSService. I created a new identical EWSService and we imported all the items into the EWSService. It started having the same error right away, so we deleted all the objects that we imported and manually reconfigured everything.  Its all working fine now and I suspected something in our import was giving us grief for all of the values in the ESW. 

I've attached the import just in case you wanted to look at what we had going on originally. 

Attachments
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore