Smart connector EVLINK - EBO

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Smart connector EVLINK - EBO
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
Sabrina_Merelli
Lieutenant Sabrina_Merelli Lieutenant
Lieutenant

Posted: ‎2021-04-13 02:21 AM

3 Likes
7
3619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-13 02:21 AM

Smart connector EVLINK - EBO

Dear Community,

do you know if someone already developed something to integrate the EVLINK in EBO with Smart Connector?

I found that in EVLINK LMS there are  REST API webservices available, so I was wondering if it is already been done something to integrate EVLINK LMS with those.

 

Thanks
Sabrina

 

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-04-13 05:50 AM

1 Like
0
3613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-13 05:50 AM

Hi Sabrina,

 

We were asked by a customer in New Zealand to develop a SmartConnector extension for EVLINK. We were told by Schneider Electric Israel that Schneider Electric is about to develop it, so we decided not to do it.

 

If SE doesn't plan to develop it we can discuss the possibility to develop it. We are based in Israel, so we will need to be able to access the EVLINK for testing purposes.

 

We have developed 3 SmartConnector extensions so far.

You may contact me at michaelm@controlsee.com.

 

Regards,

 

Michael Meirovitz   

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
SteveGregory
Commander SteveGregory Commander
Commander

Posted: ‎2021-06-10 01:00 AM

1 Like
2
3572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-10 01:00 AM

The UK team are currently building a SmartConnector that uses the native OCPP protocol to integrate with the EV chargers. Not sure on the ETA, reach out to the ISCUK team.

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 7
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-04-13 05:50 AM

1 Like
0
3614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-13 05:50 AM

Hi Sabrina,

 

We were asked by a customer in New Zealand to develop a SmartConnector extension for EVLINK. We were told by Schneider Electric Israel that Schneider Electric is about to develop it, so we decided not to do it.

 

If SE doesn't plan to develop it we can discuss the possibility to develop it. We are based in Israel, so we will need to be able to access the EVLINK for testing purposes.

 

We have developed 3 SmartConnector extensions so far.

You may contact me at michaelm@controlsee.com.

 

Regards,

 

Michael Meirovitz   

Tags (1)
  • Tags:
  • english
Reply
SteveGregory
Commander SteveGregory Commander
Commander

Posted: ‎2021-06-10 01:00 AM

1 Like
2
3573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-10 01:00 AM

The UK team are currently building a SmartConnector that uses the native OCPP protocol to integrate with the EV chargers. Not sure on the ETA, reach out to the ISCUK team.

Tags (1)
  • Tags:
  • english
Reply
Jiahau_Sin
Ensign Jiahau_Sin Ensign
Ensign

Posted: ‎2021-09-07 02:30 AM

1 Like
2
3533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-07 02:30 AM

EVlink Smart Connector development has been completed.  However, I am not sure about EVlink LMS.

 

@Sabrina_Merelli 

Tags (1)
  • Tags:
  • english
Reply
Sabrina_Merelli
Lieutenant Sabrina_Merelli Lieutenant
Lieutenant

Posted: ‎2021-10-08 08:48 AM

0 Likes
1
3517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-08 08:48 AM

Hi,

thanks for the update. It's possible to test it? It's already buyable? I can not find it yet on shop.exchange nor on smartconnectorserver portal.

Thanks again

Sabrina

Tags (1)
  • Tags:
  • english
Reply
Jiahau_Sin
Ensign Jiahau_Sin Ensign
Ensign

Posted: ‎2021-10-24 11:52 PM

1 Like
0
3492
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-24 11:52 PM

Hi Sabrina, 

 

The smart Connector is not officially launch yet.

 

But you can approach Christia Ioannou for a demo version.

 

Thanks

 

Tags (1)
  • Tags:
  • english
Reply
GrzegorzLuba
Admiral | EcoXpert Master GrzegorzLuba Admiral | EcoXpert Master
Admiral | EcoXpert Master

Posted: ‎2023-01-19 01:26 AM

0 Likes
1
2767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-19 01:26 AM

Hi @SteveGregory 

 

do you have any information about OCPP smart connector or other information how to integrate OCPP to BMS?

Reply
VaidasM
Lieutenant JG VaidasM
Lieutenant JG

Posted: ‎2024-04-28 11:49 PM

0 Likes
0
1926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-28 11:49 PM

Hello, 

do you have any news about this topic?

 

Thank you.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore