Smart Connector - Semantic tagging

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Smart Connector - Semantic tagging
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
esari
esari Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-02-17 11:37 PM . Last Modified: ‎2022-04-28 06:49 AM

1 Like
5
2422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-17 11:37 PM

Smart Connector - Semantic tagging

Hello

 

I have create semantic tagging to EBO 2022. How can I accees it from Smart Connector?

 

I have found folder

{
"Name": "Ontology Graph",
"Description": "https://brickschema.org/schema/Brick#Class",
"Type": 3,
"ParentId": "00/eValvomo",
"Id": "40https://brickschema.org/schema/Brick#Class"
}

 

But I dont know what to do next.

 

If I understand correcly. Third party company could use semantic tagging structure to browse to point or trend log and they don't need to know actual SBO path. Is this correct?

 

--

Esa

 

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-02-18 06:42 AM

0 Likes
1
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-18 06:42 AM

Semantic metadata needs to be enabled in EWS Server Configuration in EBO2022:

 

semantic enable.png

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 5
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-02-18 12:08 AM

0 Likes
2
2420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-18 12:08 AM

Hi Esa,

 

Semantic tagging in EBO is new and is a pretty big topic and there should be documentation out soon describing the EBO and EWS implementation, and the Smartconnector interface to the graph.

 

Smartconnectors interface to the graph is heavily dependent on the EWS implementation, which works like this:

 

You can navigate the graph by doing GetContainerItems calls on semantic nodes, denoted by the prefix "40". This call will return any relations that node has. That way you can navigate the graph and look for nodes that interest you. Those nodes can have relationships to EBO items, which you can fetch normally using normal GetItems calls using their EWS Id.

 

In SmartConnector GetContainerItems is used by GET/Containers/Children, so in your case a call to

 

GET/Containers/Children with Id "40https://brickschema.org/schema/Brick#Class"

 

would give you all nodes related to the base brick class and would be a good starting point.

 

You can also do the reverse using the "includeMetadata" query parameter on EBO objects. If an EBO object has a semantic relation connected to it, you will get it in the form of metadata connected to the object. There is also a new /Metadata endpoint on each enitity type where applicable if you are only interested in the semantic metadata of an EBO object. This way you can ask "What does this represent" type questions on EBO objects and if the point is tagget, you will know it's a "Supply temperature sensor" or whatever it is.

 

Hope this helps

Armend

 

Tags (1)
  • Tags:
  • english
Reply
esari
esari Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-02-18 03:23 AM

0 Likes
1
2412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-18 03:23 AM

Hello

 

 

I try to get children from that node, but I didn't receive anything. I got response:

 

{
"Message": "Container Id 40https://brickschema.org/schema/Brick#Class not found"
}

 

I have create Semantic 'Site' which has location 'Building' which have location 'Floor' which have 'Conference Room' which has point 'Temperature'.

 

Do I need to create some semantic 'root' object which can be found from "40https://brickschema.org/schema/Brick#Class" ?

 

--

Esa

 

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-02-18 04:05 AM

0 Likes
0
2409
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-18 04:05 AM

Hi Esa, 

 

That should work if I'm not wrong. Are you URL encoding the ID? You can use this:

 

https://meyerweb.com/eric/tools/dencoder/

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-02-18 06:42 AM

0 Likes
1
2403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-18 06:42 AM

Semantic metadata needs to be enabled in EWS Server Configuration in EBO2022:

 

semantic enable.png

Tags (1)
  • Tags:
  • english
Reply
esari
esari Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-02-20 10:33 PM

1 Like
0
2398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-20 10:33 PM

Hello

 

Yes.

It was that new EWS Server setting. After enabling that "Enable Semantics" settings I was able to get semantic tagging with GET Container Children from id "40https://brickschema.org/schema/Brick#Class".

 

--

Esa

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore