Reading json file from SmartConnector

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Reading json file from SmartConnector
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
sesa237670_brid
sesa237670_brid Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2018-05-21 09:43 AM

0 Likes
2
1220
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-05-21 09:43 AM

Reading json file from SmartConnector

Hi Jeff,

I have developed a UpdateProcessor that reads Google calendar using Google Restful API. For that, it reads a ‘client_secret.json’ file from my machine.  This SmartConnector works from Test Explorer in developer studio.

However, when I deploy it on the SmartConnector Portal on my machine. The Update Processor expects file in C:\windows\System32 folder.  I copy the file to that folder but getting System.IO.FileNotFoundException:

“System.IO.FileNotFoundException: Could not find file 'C:\windows\system32\client_secret.json'.

File name: 'C:\windows\system32\client_secret.json'    at System.IO.__Error.WinIOError(Int32 errorCode, String maybeFullPath)

   at System.IO.FileStream.Init(String path, FileMode mode, FileAccess access, Int32 rights, Boolean useRights, FileShare share, Int32 bufferSize, FileOptions options, SECURITY_ATTRIBUTES secAttrs, String msgPath, Boolean bFromProxy, Boolean useLongPath, Boolean checkHost)

   at System.IO.FileStream..ctor(String path, FileMode mode, FileAccess access)

   at SmartConnector.Extension.RCSI.UpdateProcessor.ReadGoogleCal()

   at SmartConnector.Extension.RCSI.UpdateProcessor.Execute_Subclass()

I try couple of things but they didn’t work either:

  1. Read the file from specific location like  “C:\RCSI” and add full physical path. Works in test Explorer but hangs in SmartConnector. Even if I stop Smartconnector service it won't release the UpdateProcessor Assembly. It release the file after a while (like 5-10 minutes).

2. Give all the permissions to the file for all the user in C:\Windows\system32. Still file not found exception.

3. I can’t change permission at system32 folder level.

I wonder if SmartConnector has any limitation imposed to read .json file. Please advise.

Thanks!

Neeraj Tomar

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2018-05-21 10:11 AM

1 Like
1
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-05-21 10:11 AM

Hi Neeraj,

First, Smart Connector has NO limitations about reading .json files. It can read anything, in fact I have done something with Google credentials .json files very recently and it worked as expected.

As you are seeing, the user who is running the Smart Connector service (by default this is the SYSTEM user), needs to have access to the file and the directory where you are storing it.

I would recommenced not hard coding the location but allowing the user to supply exactly where they want the file to be. I also recommend, setting the default to something like ProgramData where you know the SYSTEM user will have access.

For example:

$"{Environment.GetFolderPath(Environment.SpecialFolder.CommonApplicationData)}\SmartConnector\ExtensionName\credentials.json"

In general, putting anything directly onto the C drive, or into the System32 folders are bad design, as both of these places are locked down pretty tight by the operating system. It may work with the test explorer in Visual Studio because Visual Studio may be running as admin and has more rights than the SYSTEM user which the Smart Connector Service is running as.

As far as the hanging, I would make sure that you are checking your CancellationToken in parts of your code that can take a long time to execute, and if the user has asked for a cancellation, then return and end the processor execution.

Regards,

-Jeff

See Answer In Context

Reply
Replies 2
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2018-05-21 10:11 AM

1 Like
1
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-05-21 10:11 AM

Hi Neeraj,

First, Smart Connector has NO limitations about reading .json files. It can read anything, in fact I have done something with Google credentials .json files very recently and it worked as expected.

As you are seeing, the user who is running the Smart Connector service (by default this is the SYSTEM user), needs to have access to the file and the directory where you are storing it.

I would recommenced not hard coding the location but allowing the user to supply exactly where they want the file to be. I also recommend, setting the default to something like ProgramData where you know the SYSTEM user will have access.

For example:

$"{Environment.GetFolderPath(Environment.SpecialFolder.CommonApplicationData)}\SmartConnector\ExtensionName\credentials.json"

In general, putting anything directly onto the C drive, or into the System32 folders are bad design, as both of these places are locked down pretty tight by the operating system. It may work with the test explorer in Visual Studio because Visual Studio may be running as admin and has more rights than the SYSTEM user which the Smart Connector Service is running as.

As far as the hanging, I would make sure that you are checking your CancellationToken in parts of your code that can take a long time to execute, and if the user has asked for a cancellation, then return and end the processor execution.

Regards,

-Jeff

Reply
sesa237670_brid
sesa237670_brid Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2018-05-21 11:07 AM

1 Like
0
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-05-21 11:07 AM

Thank you for your response. I used the 'SpecialFolder.CommonApplication' path that fixed reading json file issue. Other issue, I was having was reading credential file from user\my documents folder. By adding logging, I figured out that reading path using below API:

System.Environment.GetFolderPath(System.Environment.SpecialFolder.Personal);

was giving me blank when the extension is deployed on the smartconnector portal. In testing environment, path was C:\Users\sesaxxx\Documents\.credentials. Changing this path also to CommonApplication folder fixed the problem.

Regards,

Neeraj Tomar

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore