The setpoints connected to the DDC MNL is going to 0 automatically upon power reset what could be the possible cause of it and is there any reference document for that concern.
Link copied. Please paste this link to share this article on your social media post.
You can create a Priority Input blocks on the MNL logic to hold the last value sent from SNVT
On this example, you can connect the nvi SNVT on I1 position