Is there a definitive list for the numbers at the beginning of StruxureWare path when using the SmartConnector Endpoint

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Is there a definitive list for the numbers at the beginning of StruxureWare path when using the SmartConnector Endpoint
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
bbradley_jaxcon
Lieutenant | EcoXpert Master bbradley_jaxcon Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-07-20 05:49 AM

0 Likes
1
1570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-20 05:49 AM

Is there a definitive list for the numbers at the beginning of StruxureWare path when using the SmartConnector Endpoint

Is there a definitive list for the numbers at the beginning of StruxureWare path when using the SmartConnector Endpoint?

For example

 

00/  - Seems to be a container

01/ - Present value

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2020-07-20 08:15 AM

2 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-20 08:15 AM

Hi Brian,

 

I can't say that there is a definitive list, but here is what I know, and most likely the majority if not all of them.

 

00 = Container Item

10 = A Value item that is a property of a Container Item

20 = Alarm Item that is a property of a Container Item

30 = History item that is a property of a Container Item

01 = Value Item

11 = Value Item that is a Property of another Value item (e.g. the priority array elements of a BACnet point)

21 = Alarm Item that is a property of a Value Item

31 = History Item that is a property of a Value Item

02 = Alarm Item

12 = Value Item that is a property of an Alarm Item

22 = Alarm item that is a property of another Alarm item

32 = History Item that is a property of an Alarm item

03 = History Item

13 = Value Item that is a property of an History Item

23 = Alarm item that is a property of a History item

33 = History Item that is a property of an another History item

 

 

For the vast majority of situations, you will be using 01, 11, 02, and 03. The others are honestly rare, and some of them I haven't actually seen, but included here for completion.

 

Best Regards,

 

-Jeff

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Reply 1
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2020-07-20 08:15 AM

2 Likes
0
1566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-20 08:15 AM

Hi Brian,

 

I can't say that there is a definitive list, but here is what I know, and most likely the majority if not all of them.

 

00 = Container Item

10 = A Value item that is a property of a Container Item

20 = Alarm Item that is a property of a Container Item

30 = History item that is a property of a Container Item

01 = Value Item

11 = Value Item that is a Property of another Value item (e.g. the priority array elements of a BACnet point)

21 = Alarm Item that is a property of a Value Item

31 = History Item that is a property of a Value Item

02 = Alarm Item

12 = Value Item that is a property of an Alarm Item

22 = Alarm item that is a property of another Alarm item

32 = History Item that is a property of an Alarm item

03 = History Item

13 = Value Item that is a property of an History Item

23 = Alarm item that is a property of a History item

33 = History Item that is a property of an another History item

 

 

For the vast majority of situations, you will be using 01, 11, 02, and 03. The others are honestly rare, and some of them I haven't actually seen, but included here for completion.

 

Best Regards,

 

-Jeff

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore