Is it possible to write to EWS log of user activity

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Is it possible to write to EWS log of user activity
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
ardak
ardak Schneider Alumni (Retired)
34
sesa180908_brid
Commander sesa180908_brid Commander
34
mike_meirovitz
Commander mike_meirovitz
21
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
sesa180961_brid
Lieutenant sesa180961_brid Lieutenant
Lieutenant

Posted: ‎2018-08-08 01:23 PM

1 Like
1
954
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-08 01:23 PM

Is it possible to write to EWS log of user activity

Hi,

I am using EWS/Smart Connector with "EwsUser1" (which is created on SBO) credentials and updating objects on SBO.

If the app/solution is being used by multiple people, would SBO log the activity being made by the app as EwsUser1?

  1. Is it possible to sent the information of the person who is making updates to SBO (via EWS/SmartConnector) so that the information of who is making updates can be tracked?
  2. Or do I have to create accounts on SBO for each user that uses the app and access EWS using their specific SBO account to have the user information in SBO logs?

Please suggest.

Tags (2)
  • Tags:
  • ews
  • smartconnector
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2018-08-08 01:29 PM

0 Likes
0
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-08 01:29 PM

Hi Maneesh,

The only 'user' information that SBO has when an EWS request is sent to it, is the user who was authenticated to make the request. Hence your case this is "EwsUser1".

There is nothing built into EWS to have a 'sub' user of sorts, the only user information is the user who is used to send the request. Therefore, there is no way to do what you are trying to do without creating multiple users in SBO, and have each user use their specific user. "EwsUser1", "EwsUser2", etc..


Regards,

-Jeff

See Answer In Context

Reply
Reply 1
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2018-08-08 01:29 PM

0 Likes
0
937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-08 01:29 PM

Hi Maneesh,

The only 'user' information that SBO has when an EWS request is sent to it, is the user who was authenticated to make the request. Hence your case this is "EwsUser1".

There is nothing built into EWS to have a 'sub' user of sorts, the only user information is the user who is used to send the request. Therefore, there is no way to do what you are trying to do without creating multiple users in SBO, and have each user use their specific user. "EwsUser1", "EwsUser2", etc..


Regards,

-Jeff

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore