Is it possible to get alarm state from Continuum points under an ASP with the SmartConnector Endpoint?

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Is it possible to get alarm state from Continuum points under an ASP with the SmartConnector Endpoint?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
ardak
ardak Schneider Alumni (Retired)
34
sesa180908_brid
Commander sesa180908_brid Commander
34
mike_meirovitz
Commander mike_meirovitz
21
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Solved
bbradley_jaxcon
Lieutenant JG bbradley_jaxcon
Lieutenant JG

Posted: ‎2020-07-16 11:09 AM

0 Likes
2
968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-16 11:09 AM

Is it possible to get alarm state from Continuum points under an ASP with the SmartConnector Endpoint?

Is it possible to get alarm state from Continuum points under an ASP with the SmartConnector Endpoint? I've tried everything that made sense to me (please refer to my last post)

 

When I use the endpoint to give me all the children in a container (GET /Containers/{id}/Children) no alarm points are returned (at least nothing that starts with a 02/) and when I poll for the value of the continuum point (GET /Values/{id}) I get no indication of the alarm status in the response.

 

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
bbradley_jaxcon
Lieutenant JG bbradley_jaxcon
Lieutenant JG

Posted: ‎2020-07-17 07:50 AM

0 Likes
0
960
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-17 07:50 AM

I got with Jeff and we discovered a way to get the alarm value for continuum alarms that are under ASPs.

Basically you can poll for the alarm value of a point instead of requesting its actual value.

 

Example:

 

Relative Humidity Continuum Point Under an ASP using the Smart Connector Endpoint (GET /Values/{id}) 

 

Path for the value : 01/Bldg26_ASP/Infinet Interface/i2NetworkB/AHU_Gym/Application/SpaceRHWest

 

Response:

{

"Name": "SpaceRHWest",

"Description": "Space Relative Humidity",

"Type": 3,

"Writeable": 1,

"Forceable": 0,

"State": 0,

"Unit": "none",

"Value": "62.0489959716797",

"ParentId": "00/Bldg26_ASP/Infinet Interface/i2NetworkB/AHU_Gym/Application", "Id": "01/Bldg26_ASP/Infinet Interface/i2NetworkB/AHU_Gym/Application/SpaceRHWest"

}

 

Path for the alarm value : 11/Bldg26_ASP/Infinet Interface/i2NetworkB/AHU_Gym/Application/SpaceRHWest/AlarmValue

 

{
"Name": "SpaceRHWest-AlarmValue",
"Description": "AlarmValue",
"Type": 5,
"Writeable": 0,
"Forceable": 0,
"State": 0,
"Unit": "none",
"Value": "0", (Value would be 1 if the point was in alarm)
"ParentId": "00/Bldg26_ASP/Infinet Interface/i2NetworkB/AHU_Gym/Application/SpaceRHWest",
"Id": "11/Bldg26_ASP/Infinet Interface/i2NetworkB/AHU_Gym/Application/SpaceRHWest/AlarmValue"
}

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2020-07-16 11:15 AM

0 Likes
1
967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-16 11:15 AM

Hi!

From what I understand, this should be possible, however at this point, I think I need to see what you are looking at to see if I can determine if there is a way, or if there might be some sort of bug in EBO.

 

Please send me an email to jeff.bowman@se.com and we can schedule a call.

 

Best Regards,

 

-Jeff

Tags (1)
  • Tags:
  • english
Reply
bbradley_jaxcon
Lieutenant JG bbradley_jaxcon
Lieutenant JG

Posted: ‎2020-07-17 07:50 AM

0 Likes
0
961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-17 07:50 AM

I got with Jeff and we discovered a way to get the alarm value for continuum alarms that are under ASPs.

Basically you can poll for the alarm value of a point instead of requesting its actual value.

 

Example:

 

Relative Humidity Continuum Point Under an ASP using the Smart Connector Endpoint (GET /Values/{id}) 

 

Path for the value : 01/Bldg26_ASP/Infinet Interface/i2NetworkB/AHU_Gym/Application/SpaceRHWest

 

Response:

{

"Name": "SpaceRHWest",

"Description": "Space Relative Humidity",

"Type": 3,

"Writeable": 1,

"Forceable": 0,

"State": 0,

"Unit": "none",

"Value": "62.0489959716797",

"ParentId": "00/Bldg26_ASP/Infinet Interface/i2NetworkB/AHU_Gym/Application", "Id": "01/Bldg26_ASP/Infinet Interface/i2NetworkB/AHU_Gym/Application/SpaceRHWest"

}

 

Path for the alarm value : 11/Bldg26_ASP/Infinet Interface/i2NetworkB/AHU_Gym/Application/SpaceRHWest/AlarmValue

 

{
"Name": "SpaceRHWest-AlarmValue",
"Description": "AlarmValue",
"Type": 5,
"Writeable": 0,
"Forceable": 0,
"State": 0,
"Unit": "none",
"Value": "0", (Value would be 1 if the point was in alarm)
"ParentId": "00/Bldg26_ASP/Infinet Interface/i2NetworkB/AHU_Gym/Application/SpaceRHWest",
"Id": "11/Bldg26_ASP/Infinet Interface/i2NetworkB/AHU_Gym/Application/SpaceRHWest/AlarmValue"
}

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of