EWS Client 2.4.10 (VB .net) - Unauthorized with client authentication scheme 'Digest'.

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • EWS Client 2.4.10 (VB .net) - Unauthorized with client authentication scheme 'Digest'.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SmartConnector Forum
Start a Topic
RvN
Ensign RvN Ensign
Ensign

Posted: ‎2019-01-04 12:49 AM . Last Modified: ‎2019-01-04 12:51 AM

0 Likes
11
3204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-01-04 12:49 AM

EWS Client 2.4.10 (VB .net) - Unauthorized with client authentication scheme 'Digest'.

I have a small visuale basic test app to sign in on an ES using the EwsClient. It works perfect with ES version 1.9.3 but when trying to connect to ES version 2.0.2 the server returns:

 

***

The HTTP request is unauthorized with client authentication scheme 'Digest'.

The authentication header received from the server was 'Digest realm="ews@SxWBM",qop="auth",algorithm="SHA-256",nonce="4459BFB53312E1CE4C0CDF0B6F7E5234",opaque="472A3A"'.

 

The remote server returned an error: (401) Unauthorized.

***

(also see attached debug log "2019-01-04.log")

 

The ES 2.0.2 EWS Server is enabled and credentials used (domain/user, password) has access via workstation sign in.

 

Class Code:

VB - EWS Session ClassVB - EWS Session Class

(also see attached VB Code file "EWSclass.txt")

 

The project refer to:

<packages>
 <package id="EntityFramework" version="6.2.0" targetFramework="net461" />
 <package id="Ews.Client" version="2.4.10" targetFramework="net461" />
 <package id="Ews.Common" version="2.4.10" targetFramework="net461" />
 <package id="Microsoft.AspNet.Identity.Core" version="2.2.1" targetFramework="net461" />
 <package id="Microsoft.AspNet.Identity.Owin" version="2.2.1" targetFramework="net461" />
 <package id="Microsoft.AspNet.WebApi.Client" version="5.2.3" targetFramework="net461" />
 <package id="Microsoft.AspNet.WebApi.Core" version="5.2.3" targetFramework="net461" />
 <package id="Microsoft.AspNet.WebApi.Owin" version="5.2.3" targetFramework="net461" />
 <package id="Microsoft.AspNet.WebApi.OwinSelfHost" version="5.2.3" targetFramework="net461" />
 <package id="Microsoft.Owin" version="3.1.0" targetFramework="net461" />
 <package id="Microsoft.Owin.Host.HttpListener" version="3.1.0" targetFramework="net461" />
 <package id="Microsoft.Owin.Hosting" version="3.1.0" targetFramework="net461" />
 <package id="Microsoft.Owin.Security" version="3.1.0" targetFramework="net461" />
 <package id="Microsoft.Owin.Security.Cookies" version="3.1.0" targetFramework="net461" />
 <package id="Microsoft.Owin.Security.OAuth" version="3.1.0" targetFramework="net461" />
 <package id="Mongoose.Common" version="2.4.10" targetFramework="net461" />
 <package id="Newtonsoft.Json" version="10.0.3" targetFramework="net461" />
 <package id="NLog" version="4.4.12" targetFramework="net461" />
 <package id="Owin" version="1.0" targetFramework="net461" />
 <package id="Swashbuckle.Core" version="5.6.0" targetFramework="net461" />
 <package id="SxL.Common" version="2.4.10" targetFramework="net461" />
 <package id="WebApiThrottle.StrongName" version="1.5.4" targetFramework="net461" />
</packages>

 

Am i missing something to configure?

 

Can anybody please help?

Attachments
2019-01-04.log
Tags (1)
  • Tags:
  • EWS Client
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2019-01-04 05:08 AM

0 Likes
6
3196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-01-04 05:08 AM

Hi!

 

In 2.0.X EWS is disabled by default. I would check to make sure that 'Enable EWS Server' in your EWS Server Configuration is set to Enabled:

 

2019-01-04_8-06-27.pngRegards,

 

-Jeff

Reply
RvN
Ensign RvN Ensign
Ensign

Posted: ‎2019-01-04 05:19 AM

0 Likes
5
3194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-01-04 05:19 AM

Hi Jeff

 

I have already done that.

 

My settings:

EBO.EWS.Settings.png

 

Regards

 

Rene

Reply
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2019-01-04 05:37 AM

0 Likes
4
3189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-01-04 05:37 AM

Hi Rene,

 

In my experience I have only seen this error when:

 

1. The credentials are actually incorrect (doesn't seem to be the case here)

2. The EWS Server is disabled (doesn't seem to be the case here)

3. So many requests have been sent without using the same session that you need to wait 5 minutes before sending more. In your case do any of your requests to 2.0 work or do none of them work?

 

Can you try a couple things?

 

1. Make sure 'Redirect web clients to https' is not checked.

2019-01-04_8-35-21.png

2. If you arent already, can you try and use the HTTPS endpoint for EWS and see if it starts working.

 

From what I see in your code, you are doing everything you need to be. 

 

Regards,

 

-Jeff

Reply
RvN
Ensign RvN Ensign
Ensign

Posted: ‎2019-01-04 06:41 AM

0 Likes
3
3187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-01-04 06:41 AM

Hi Jeff

 

1. These are my current Security settings:

EBO.SECURITY.SET.png

 

2. I have tried HTTP and HTTPS endpoint (with fails) but I am able to log on from Workstation and Webstation with both HTTP and HTTPS.

 

It doesn't matter if I wait an hour with a retry.

 

Result of declaring New EwsClient conneting to 2.0.2 [ERROR]:

TEST.EWS.ERROR.png

 

Result of declaring New EwsClient conneting to 1.9.3 [SUCCESS]:

TEST.EWS.NOERROR.PNG

 

Regards

 

Rene

Reply
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2019-01-04 07:06 AM

0 Likes
2
3185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-01-04 07:06 AM

Hi Rene,

 

As far as I know there should be no difference between 1.9.3 and 2.0.x as far as connecting via EWS (I have used the EWS Client from SmartConnector on both many many times with success)

 

Can you try and download SOAPUI and use it to try and send a GetWebServiceInformation request to your server? I would be interested to see if this works. If it does, I may need to get on a debug call with you for what you are doing.. If it doesn't work there either.. It is likely a problem with your EBO installation or configuration.. But at the moment I am not sure what would be the cause of that is the case.

 

Regards,

 

-Jeff

Reply
RvN
Ensign RvN Ensign
Ensign

Posted: ‎2019-01-07 05:14 AM

0 Likes
1
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-01-07 05:14 AM

Hi Jeff

 

I have installed SoapUI (Open Source version) and configured as below

SOAPUI.PNG

 

I am completely NOOP in configuring HTTP REST request via API's so could you guide me on how to send a GetWebServiceInformation?

 

Regards

 

Rene

Reply
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2019-01-07 05:36 AM

0 Likes
0
3177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-01-07 05:36 AM

Hi Rene,

 

 

Please send me an email at jeff.bowman@se.com and I will help you set this up.

 

Regards,

 

-Jeff

Reply
Sabrina_Merelli
Lieutenant Sabrina_Merelli Lieutenant
Lieutenant

Posted: ‎2020-06-23 03:19 AM

1 Like
2
3118
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-23 03:19 AM

Hi

I have the same problem, I am trying to connect with a Smart connector to the EWS of EBO, I receive the same error.

Already checked the credentials, they are correct.

Have you solved the problem? How?

 

Thanks

Sabrina

Tags (1)
  • Tags:
  • english
Reply
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2020-06-23 05:29 AM

1 Like
1
3116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-23 05:29 AM

Hi Sabrina,

 

One thing to verify is that the credentials you are using are using the default domain in EBO. In order to use EWS, the user must be in the default domain. Can you check if this is the case in your scenario?

 

Also, are you able to get it to work at all? There is also a known issue where it will seemingly work for a while, and then stop working. 

 

Best Regards,

 

-Jeff

Tags (1)
  • Tags:
  • english
Reply
Sabrina_Merelli
Lieutenant Sabrina_Merelli Lieutenant
Lieutenant

Posted: ‎2020-06-29 01:26 AM

0 Likes
0
3111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-29 01:26 AM

Thanks Jeff,

I thought we were in the second scenario, as it worked for a while and then stopped.

it seems instead we solved unchecking the option "Redirect web clients to https" from the workstation. 

I hope it will last...

 

Thanks

Best Regards

Sabrina 

Tags (1)
  • Tags:
  • english
Reply
SteveGregory
Commander SteveGregory Commander
Commander

Posted: ‎2021-02-17 02:17 AM

0 Likes
0
3078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-17 02:17 AM

@JeffBowman is this the same issue I had with the missing StruxureMap files? I had a similar issue with a console app that i made, outside of the SmartConnector framework and had the same errors. It worked with EBO 1.9 but not 3.0. It was due to the fact that the EwsClient in the Nuget package actually has a dependency on the StructureMap and StructureMap.Net4 files which are found in the SmartConnector folder. There was one other file too but I don't recall which one. Adding a reference to these three files in my console app fixed my issue.

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore