EBO-OPC Server Integration

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • EBO-OPC Server Integration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
ardak
ardak Schneider Alumni (Retired)
34
sesa180908_brid
Commander sesa180908_brid Commander
34
mike_meirovitz
Commander mike_meirovitz
21
View All
Related Products
product field
Control-See Software Solutions Ltd
OPC Server for Building Operations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Solved
AdamC31
Crewman AdamC31
Crewman

Posted: ‎2023-05-16 05:30 AM . Last Modified: ‎2025-05-29 11:31 PM

0 Likes
4
2175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-16 05:30 AM

EBO-OPC Server Integration

Hi All, 

 

Currently in the process of integrating a number of EBO sites (5 sites) via the EBO-OPC Server product from ControlSee (The product is available on Controlsee website) into a central monitoring systems (Aveva). If in a years time site no.1 add a new chiller for instance and there are new alarms configured on the EBO headend. Does the ControlSee application automatically pick these points up or do these also need configuring/engineering?

 

TIA!

Adam

  • Thumbnail of OPC Server for Building Operations
    Control-See Software Solutions Ltd
    OPC Server for Building Operations
View products (1)
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2023-05-16 05:43 AM

0 Likes
2
2170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-16 05:43 AM

Hi Adam,

 

When you add a new alarm in the EBO, there is  o need for configuration/engineering. All you need is to add the new alarm in the OPC Client (Aveva in your case). For example, if the alarm id is "/Server 1/Values/Change of State Alarm", you need to add this OPC item in Aveva - "/Server 1/Values/Change of State Alarm.Alarm".

 

Michael

See Answer In Context

Reply
Replies 4
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2023-05-16 05:43 AM

0 Likes
2
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-16 05:43 AM

Hi Adam,

 

When you add a new alarm in the EBO, there is  o need for configuration/engineering. All you need is to add the new alarm in the OPC Client (Aveva in your case). For example, if the alarm id is "/Server 1/Values/Change of State Alarm", you need to add this OPC item in Aveva - "/Server 1/Values/Change of State Alarm.Alarm".

 

Michael

Reply
AdamC31
Crewman AdamC31
Crewman

Posted: ‎2023-05-17 01:46 AM

0 Likes
0
2158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-17 01:46 AM

Thank you very much for the confirmation

Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2023-05-18 04:00 AM

0 Likes
0
2135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-18 04:00 AM

Al,

 

My mistake. You need to do run the Discovery processor in SmartConnector to discover the newly added alarms.

 

Regards,

 

Mike

Reply
killu7
killu7
Cadet

Posted: ‎2023-05-24 06:19 AM

0 Likes
0
2100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-24 06:19 AM

Right click on the OPC DataHub system-tray icon and choose Properties. In the Properties window, select OPC .

regards: ultrasonic pest repeller side effects

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now