Release Notes for Smart-UPS Ultra 5-20 kW Firmware v3.3.0.8

Smart-UPS Ultra 5-20 kW

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Network Management Cards
  • Network Management Card 3
  • Smart-UPS Ultra 5-20 kW
  • Release Notes for Smart-UPS Ultra 5-20 kW Firmware v3.3.0.8
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

NMC Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Smart-UPS Ultra 5-20 kW
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1427 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Release Notes for Smart-UPS Ultra 5-20 kW Firmware v3.3.0.8

Lt. Commander SwathiNaidu Lt. Commander
‎2025-03-03 12:44 AM

Affected Revision Levels

 

Component  File Details
Smart-UPS Ultra 5-20 kW Application Windows:
snst_nmc3_sucan_3-3-0-8.exe
Linux & macOS: 
snst_nmc3_sucan_3-3-0-8.tar.gz
UPS Application for Smart-UPS Ultra 5-20 kW.

 

To upgrade to firmware version 3.0 or later, the only supported method is the Secure NMC System (SNS) Tool, which can be downloaded from www.se.com/secure-nmc or by searching for SFNMC3FMTSUCAN. To access the firmware in the software, a valid Secure NMC subscription is required. For more information, see the SNS Tool User Guide.

 

SwathiNaidu_0-1718792359613.pngIf you downgrade from firmware version 2.4+ to a firmware version lower than 2.4, this will cause the card to be formatted, erasing all security certificates, encryption keys, configuration settings, and the event and data logs.

 

New Features

 

New Feature

UPS Family
SRTL Devices SRYL Devices

Command Line Interface (CLI) added to the Web UI under Control > Network > Web CLI.

♦ ♦

IPv6 functionality is improved.

♦ ♦

Added support for smart Service Bypass Unit.

  ♦

The display now fully supports the lights/beeper test.

  ♦

Added display support for Efficiency Test Mode.

  ♦

 

Fixed Issues

 

Fixed Issue

UPS Family

SRTL

Devices

SRYL

Devices

The LDAP TLS connection now works as expected when connecting to an IP address and server certificate using SAN type "iPAddress".

♦

♦

DHCPv6 no longer intermittently reboots when the network interface starts or when the Ethernet cable is reseated.

♦

 ♦

Improved logging for account disabled events.

♦

 ♦

The expiration date of self-signed certificates has been updated.

 ♦

♦

You can now send emails as expected if the SMTP server uses an IPv6 address.

 ♦

♦

The severity of Syslog-related events in the configuration file has been corrected.

 ♦

♦

The NMC now supports the latest set of UPS alarms with the correct severity and improved alarm messages.

 ♦

♦

The alarm description is now shown correctly in DCE for outlet group-related alarms.

 ♦

 

Security Update

The following third-party components (open source or proprietary) have been updated to address cybersecurity vulnerabilities:

  • RADIUS Protocol under RFC 2865 - CVE-2024-3596

Implemented support for the Message-Authenticator attribute.

♦ ♦

The following security vulnerability has been addressed in this release:

  • CWE-1285: Improper Validation of Specified Index, Position, or Offset in Input

Fixed an improper user input validation.

♦ ♦

 

Known Issues

 

Known Issue UPS Family

SRTL

Devices

SRYL

Devices

After updating the NMC’s firmware via a USB flash drive, the USB is not recognized in the display or NMC Web UI. ♦ ♦
Some pages in the Web UI help are not updated. ♦ ♦
It can take up to 30 minutes to complete a UPS firmware upgrade when using HTTPS. To workaround this, use SCP as an alternative. ♦ ♦
When a UPS firmware upgrade is in progress, the upsAdvcontrolFirmwareUpdate SNMP OID incorrectly reports the value as “noFirmwareUpdate” instead of “UpdateinProgress”. ♦ ♦
Filtering by time does not work for the Power Event Log. ♦ ♦
Entering unsupported commands in the Command Line Interface (CLI) does not return a E102 Parameter error. ♦ ♦
You cannot unzip the debug file completely from a USB drive. This issue is seen intermittently. ♦  
You are unable to configure upsAdvConfigAlarmRedundancy OID from SNMP interface.   ♦
When an internal or external Battery Module is connected or disconnected from its slot, the Event Log entry does not report its serial number.   ♦
You cannot make configuration changes via the display when RADIUS is enabled and the User Mode is set to “Authentication Needed”.   ♦
The option to cancel or mute a UPS audible alarm is not present in the Web UI.   ♦
The ups -s start CLI command is unsuccessful even when the self-test is started correctly.   ♦
There is no option to set the language of the display in the NMC Web UI.   ♦
You cannot modify the output voltage setting from the SNMP interface if the output is in Manual Bypass.   ♦

 

 

Secure NMC System (SNS) Tool for Smart-UPS Ultra Hash Signatures

 

Windows

Signatures

snst_nmc3_sucan_3-3-0-8.exe

CRC32

2287D7E8

CRC64

BD2BB46FE19880C7

SHA-256

784095DFECA1F011FBDC4AACF97D3EE311FEC20AD3794BD37597514248871E2D

SHA-1

95956FDC1D54E5A4161197D192362AE00F8542A5

BLAKE2sp

A7D04B3AE3432AA17751FDF8B785706692D993CBDCC27BEA775187610CADE644

 

 

Linux

Signatures

snst_nmc3_sucan_3-3-0-8.tar.gz

CRC32

DE3EAC04

CRC64

8A680C99FFFE53BE

SHA-256

7B3A42CC0E67C5C5E24B36CC65CD97F8823484DA07EFDBDCA269136E7787179C

SHA-1

52E868554F1200179BC907A7CE68B6B6C9739C33

BLAKE2sp

C70D6540D9B60E833A8E6D77036C75C50A97CF7804F6A0EF5A02068A219E6A02

 

 

 

macOS

Signatures

snst_nmc3_sucan_3-3-0-8.tar.gz

CRC32

428EB57D

CRC64

ABBA1AA4129247E0

SHA-256

A6A4DC96FCAB00B967B9906392E5237F798D84E0427EBBF84CBA1ED35F6D62FD

SHA-1

83ACC8A455C6922C217B54D42E1720CA9F6ABF81

BLAKE2sp

F6818C9DB6FA17D2D70AD9ECFC6A489F289D8E7A684482272B8E22E74E54E0FD

 

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore