Release Notes for Smart-UPS Ultra 5-20 kW Firmware v3.0.1.4


on 2024-06-13 08:21 AM
Affected Revision Levels
Component | File | Details |
Smart-UPS Ultra Application | apc_hw21_sucan_3-0-1-4.nmc3 | UPS Application for Smart-UPS Ultra 5-20 kW. |
For details on upgrading the UPS Network Management Card 3 (NMC 3) firmware, see the NMC3 User Guide.
New Features
New Feature |
UPS Family | |
SRTL Devices | SRYL Devices | |
The NMC3 platform and Smart-UPS Ultra 5-20kW application are now IEC 62443-4-2 certified. | ♦ | ♦ |
Support added for audit logging to ensure control actions and configuration changes are recorded in the Event Log. | ♦ | ♦ |
Support added for remote authentication via the TACACS+ protocol. | ♦ | ♦ |
Security Update | ||
Password security has been updated to align with the requirements for IEC 62443-4-2. By default, passwords now need to be a minimum of 8 characters in length (strong password setting enabled). | ♦ | ♦ |
Fixed Issues
Fixed Issue |
UPS Family |
|
SRTL Devices |
SRYL Devices |
|
The NMC3 Web UI now allows passwords with up to 64 characters, as expected. |
♦ |
♦ |
For encrypted email settings, install CA certificate to the certificate store and set Require CA Root Certificate correctly. |
♦ |
♦ |
Improved TLS certificate for email. |
♦ |
♦ |
The NMC3 Web UI now allows the Battery Install date setting and other general UPS settings. |
♦ |
♦ |
The correct On Battery status message will now appear on the Web UI Home page for Japanese. |
♦ |
♦ |
The NMC now supports the latest set of UPS alarms with the correct severity and improved alarm messages. |
♦ |
♦ |
Partially written files can now be recovered after a system reset event. |
♦ |
♦ |
The Power Module Fault now appears correctly on the SNMP interface. |
|
♦ |
Improved Japanese translations for the display. |
|
♦ |
Able to set the OIDs |
|
♦ |
Security Update |
||
The following security vulnerabilities have been addressed in this release:
|
♦ |
♦ |
Known Issues
Known Issue | UPS Family | |
SRTL Devices |
SRYL Devices |
|
After updating the NMC’s firmware via a USB flash drive, the USB is not recognized in the display or NMC Web UI. | ♦ | ♦ |
Some pages in the Web UI help are not updated. | ♦ | ♦ |
It can take up to 30 minutes to complete a UPS firmware upgrade when using HTTPS. To workaround this, use SCP as an alternative. | ♦ | ♦ |
The alarm description is shown incorrectly in DCE for outlet group-related alarms. | ♦ | |
You cannot unzip the debug file completely from a USB drive. This issue is seen intermittently. | ♦ | |
When a UPS firmware upgrade is in progress, the upsAdvcontrolFirmwareUpdate SNMP OID incorrectly reports the value as “noFirmwareUpdate” instead of “UpdateinProgress”. | ♦ | |
Filtering by time does not work for the Power Event Log. | ♦ | |
Entering unsupported commands in the Command Line Interface (CLI) does not return a E102 Parameter error. | ♦ | |
You are unable to configure upsAdvConfigAlarmRedundancy OID from SNMP interface. | ♦ | |
Only alphanumeric passwords are supported for new users created in the NMC for access to the display. | ♦ | |
When an internal or external Battery Module is connected or disconnected from its slot, the Event Log entry does not report its serial number. | ♦ | |
You cannot make configuration changes via the display when RADIUS is enabled and the User Mode is set to “Authentication Needed”. | ♦ | |
The option to cancel or mute a UPS audible alarm is not present in the Web UI. | ♦ | |
The ups -s start CLI command is unsuccessful even when the self-test is started correctly. | ♦ | |
There is no option to set the language of the display in the NMC Web UI. | ♦ | |
There is no option in the Web UI or the display to cancel a UPS audible alarm test. It is not recommended to initiate a continuous alarm as the only way to stop the UPS beeping is to turn off the UPS. | ♦ | |
You cannot modify the output voltage setting from the SNMP interface if the output is in Manual Bypass. | ♦ | |
The “Minimum Redundancy lost" event is not displayed in PowerChute Network Shutdown although it is supported by the NMC. If this event occurs, the server will not shutdown. | ♦ |
Secure NMC System (SNS) Tool for Smart-UPS Ultra Hash Signatures
Signatures | snst_nmc3_sucan_3-0-1-4-v2.exe |
CRC32 | B912E432 |
CRC64 | 80C0307FA16E865B |
SHA-256 | DC256451913BE8FA1DCD63E3205DBEA012D83C4FA82E5610BEE2864F3CBD4C61 |
SHA-1 | B03DB85215D2500EE3C71FB48714259557AD3173 |
BLAKE2sp | A49568C6AA16E7BFDBD9E99F6FF9123AE5532FFB8D4304B2223631801ABA2C79 |
Link copied. Please paste this link to share this article on your social media post.