For details on upgrading the UPS Network Management Card 3 (NMC 3) firmware, see the NMC3 User Guide.
New Features
New Feature
UPS Family
SRTL Devices
SRYL Devices
The NMC3 platform and Smart-UPS Ultra 5-20kW application are now IEC 62443-4-2 certified.
♦
♦
Support added for audit logging to ensure control actions and configuration changes are recorded in the Event Log.
♦
♦
Support added for remote authentication via the TACACS+ protocol.
♦
♦
Security Update
Password security has been updated to align with the requirements for IEC 62443-4-2. By default, passwords now need to be a minimum of 8 characters in length (strong password setting enabled).
♦
♦
Fixed Issues
Fixed Issue
UPS Family
SRTL
Devices
SRYL
Devices
The NMC3 Web UI now allows passwords with up to 64 characters, as expected.
♦
♦
For encrypted email settings, install CA certificate to the certificate store and set Require CA Root Certificate correctly.
♦
♦
Improved TLS certificate for email.
♦
♦
The NMC3 Web UI now allows the Battery Install date setting and other general UPS settings.
♦
♦
The correct On Battery status message will now appear on the Web UI Home page for Japanese.
♦
♦
The NMC now supports the latest set of UPS alarms with the correct severity and improved alarm messages.
♦
♦
Partially written files can now be recovered after a system reset event.
♦
♦
The Power Module Fault now appears correctly on the SNMP interface.
♦
Improved Japanese translations for the display.
♦
Able to set the OIDs upsAdvConfigHighBypassLLTransferVolt upsAdvConfigLowBypassLLTransferVolt from SNMP interface.
♦
Security Update
The following security vulnerabilities have been addressed in this release:
CWE-74: Improper neutralization of special elements in output used by a downstream component (Injection).
CWE-79: Improper neutralization of input during web page generation (Cross-site Scripting).
♦
♦
Known Issues
Known Issue
UPS Family
SRTL
Devices
SRYL
Devices
After updating the NMC’s firmware via a USB flash drive, the USB is not recognized in the display or NMC Web UI.
♦
♦
Some pages in the Web UI help are not updated.
♦
♦
It can take up to 30 minutes to complete a UPS firmware upgrade when using HTTPS. To workaround this, use SCP as an alternative.
♦
♦
The alarm description is shown incorrectly in DCE for outlet group-related alarms.
♦
You cannot unzip the debug file completely from a USB drive. This issue is seen intermittently.
♦
When a UPS firmware upgrade is in progress, the upsAdvcontrolFirmwareUpdate SNMP OID incorrectly reports the value as “noFirmwareUpdate” instead of “UpdateinProgress”.
♦
Filtering by time does not work for the Power Event Log.
♦
Entering unsupported commands in the Command Line Interface (CLI) does not return a E102 Parameter error.
♦
You are unable to configure upsAdvConfigAlarmRedundancy OID from SNMP interface.
♦
Only alphanumeric passwords are supported for new users created in the NMC for access to the display.
♦
When an internal or external Battery Module is connected or disconnected from its slot, the Event Log entry does not report its serial number.
♦
You cannot make configuration changes via the display when RADIUS is enabled and the User Mode is set to “Authentication Needed”.
♦
The option to cancel or mute a UPS audible alarm is not present in the Web UI.
♦
The ups -s start CLI command is unsuccessful even when the self-test is started correctly.
♦
There is no option to set the language of the display in the NMC Web UI.
♦
There is no option in the Web UI or the display to cancel a UPS audible alarm test. It is not recommended to initiate a continuous alarm as the only way to stop the UPS beeping is to turn off the UPS.
♦
You cannot modify the output voltage setting from the SNMP interface if the output is in Manual Bypass.
♦
The “Minimum Redundancy lost" event is not displayed in PowerChute Network Shutdown although it is supported by the NMC. If this event occurs, the server will not shutdown.
♦
Secure NMC System (SNS) Tool for Smart-UPS Ultra Hash Signatures