Release Notes for Smart-UPS Ultra 5-20 kW Firmware v2.5.1.3


Affected Revision Levels
Component | File | Details |
Smart-UPS Ultra Application | apc_hw21_sucan_2-5-1-3.nmc3 | UPS Application for Smart-UPS Ultra 5-20 kW. |
For details on upgrading the UPS Network Management Card 3 (NMC 3) firmware, see the NMC3 User Guide.
New Features
New Feature |
UPS Family | |
SRTL Devices | SRYL Devices | |
Support added for Dell VxRail. | ♦ | ♦ |
Support added for new Smart-UPS Ultra devices SRTL8KRM4UI and SRTL10KRM4UI, both devices have Switched Outlet Groups. | ♦ | ♦ |
Display screen improvements. See the Fixed Issues section for more details. |
♦ | |
Support added for Smart-UPS Modular Ultra devices SRYL13KRMM and SRYL18KRMM. | ♦ | |
The NMC now supports UPS firmware updates while the UPS is in Manual Bypass mode. | ♦ | |
The system now allows the setting of Output Voltage when the output is in Manual Bypass. | ♦ |
Fixed Issues
Fixed Issue |
UPS Family |
|
SRTL Devices |
SRYL Devices |
|
The data log values were updated for kW and kVA. |
♦ |
♦ |
You can now set the Output Frequency Slew Rate from the Web UI. |
♦ |
♦ |
Always acceptable and Never acceptable options were added in SNMP to the upsAdvConfigBypassPhaseLockRequired OID. |
♦ |
♦ |
The location of internal battery modules are now also displayed in the Web UI. |
♦ |
♦ |
UPS firmware upgrades work as expected if initiated via the NMC in the SmartSlot. |
♦ |
♦ |
The UPS Event Log now displays battery frame information when battery modules are removed or installed. |
♦ |
♦ |
The NMC now supports the latest set of UPS alarms with the correct severity. |
♦ |
♦ |
The default baud rate was changed to 9600 for UIO serial port |
♦ |
|
The NMC no longer reports lost communications for 30-50 seconds. |
♦ |
|
The Power Module Fault message now includes the faulted power module location. |
|
♦ |
The NMC and its display will now reboot after performing ‘Reset all Exclude TCP/IP’. |
|
♦ |
After setting the IP address manually via the display, the NMC and its display now reboots automatically as expected. |
|
♦ |
The UPS status is now correctly shown in the display when the UPS is in Software Bypass and Temporary Bypass modes. |
|
♦ |
When the UPS is in Error condition, the UPS status now correctly reports the Error state on the display. |
|
♦ |
Saving the Debug Log on a USB drive will now provide the full set of files as expected. |
|
♦ |
Line-to-Line output voltage is now reported in the NMC data log. |
|
♦ |
The reported load percentage on the display’s home screens is no longer dependent on the redundancy setting and always uses the N+0 value. |
|
♦ |
When the display access is disabled, the user cannot log in on the display. |
|
♦ |
The Status > UPS > Output screen on the display has been updated to always show the percent power values at N+0 regardless of the redundancy setting. |
|
♦ |
The minimum to maximum range data has been removed from the display configuration screens. |
|
♦ |
When the UPS is off without an error condition, the display will now show ‘Output Off’ as expected. |
|
♦ |
The Status > UPS > Overview screen on the display is now redesigned for localization support. |
|
♦ |
On the display, the USB menu will now show as expected after |
|
♦ |
Following a successful UPS firmware upgrade via a USB drive, USB-related options under the Configuration > USB screen are now available in the display. |
|
♦ |
The CLI now allows you to change the redundancy alarm setting via cfgpower -red command. |
|
♦ |
Known Issues
Known Issue | UPS Family | |
SRTL Devices |
SRYL Devices |
|
After updating the NMC’s firmware via a USB flash drive, the USB is not recognized in the display or NMC Web UI. | ♦ | ♦ |
Some pages in the Web UI help are not updated. | ♦ | ♦ |
It can take up to 30 minutes to complete a UPS firmware upgrade when using HTTPS. To workaround this, use SCP as an alternative. | ♦ | ♦ |
The alarm description is shown incorrectly in DCE for outlet group-related alarms. | ♦ | |
You cannot unzip the debug file completely from a USB drive. This issue is seen intermittently. | ♦ | |
When a UPS firmware upgrade is in progress, the upsAdvcontrolFirmwareUpdate SNMP OID incorrectly reports the value as “noFirmwareUpdate” instead of “UpdateinProgress”. |
♦ | |
Filtering by time does not work for the Power Event Log. | ♦ | |
Entering unsupported commands in the Command Line Interface (CLI) does not return a E102 Parameter error. | ♦ | |
You are unable to configure some OIDs upsAdvConfigAlarmRedundancy, upsAdvConfigHighBypassLLTransferVolt, upsAdvConfigLowBypassLLTransferVolt from SNMP interface. |
♦ | |
Only alphanumeric passwords are supported for new users created in the NMC for access to the display. | ♦ | |
When an internal or external Battery Module is connected or disconnected from its slot, the Event Log entry does not report its serial number. | ♦ | |
You cannot make configuration changes via the display when RADIUS is enabled and the User Mode is set to “Authentication Needed”. | ♦ | |
The option to cancel or mute a UPS audible alarm is not present in the Web UI. | ♦ | |
The ups -s start CLI command is unsuccessful even when the self-test is started correctly. | ♦ | |
There is no option to set the language of the display in the NMC Web UI. | ♦ | |
There is no option in the Web UI or the display to cancel a UPS audible alarm test. It is not recommended to initiate a continuous alarm as the only way to stop the UPS beeping is to turn off the UPS. | ♦ | |
You cannot modify the output voltage setting from the SNMP interface if the output is in Manual Bypass. | ♦ | |
The “Minimum Redundancy lost" event is not displayed in PowerChute Network Shutdown although it is supported by the NMC. If this event occurs, the server will not shutdown. | ♦ |
Hash Signatures
Signatures | apc_hw21_sucan_2-5-1-3.exe |
CRC32 | 2B309B2E |
CRC64 | DF6A37B237A23FC4 |
SHA-256 | 0E6A13148CBD3EF5C860A7FA11713B3BB3416B0FF0DD8F59E613ACEC0D2A4FFB |
SHA-1 | C54FA1BA2349383C3FB9FABBEE752C534804F868 |
BLAKE2sp | 98F421FE6BF7823CA77518E42E557E84EA3D0F97DAEBFB74AFA8E7882237CCFA |