Hi,
As I know, there is some input requirement for "Trip circuit supervision with two digital inputs".
If I design the control circuit with "Trip circuit supervision with two combined digital inputs",
do I need to select a lower switching threshold or reverse the polarity of digital input?
BR
Johnny
Link copied. Please paste this link to share this article on your social media post.
Dear Mr. Johnny Sun
If you are using trip circuit supervision with 2 digital inputs, then you need to select a lower switching threshold voltage. The relay ordering code will have options to choose the operating voltages for the first 2 Digital inputs.
Regards
Karthik.P
Regards
Karthik.P
Link copied. Please paste this link to share this article on your social media post.
Dear Karthik.P
Thanks for your comments.
For using trip circuit supervision with 2 digital inputs, the description is very clear in P3 series user manual.
Two DIs are connected in series.
Another 2 digital inputs type:
Two DIs are connected in parallel.
It is called " Trip circuit supervision with two combined digital inputs" in the user manual.
I can not find the detial information of those digital inputs.
Kindly refer to the attached .JPG file.
BR
Johnny
Link copied. Please paste this link to share this article on your social media post.
Dear Mr. Johnny Sun
If you are choosing 'Trip circuit supervision with two combined digital inputs' then you no need to select a digital input with lower pickup threshold setting.
Regards
Karthik.P
Link copied. Please paste this link to share this article on your social media post.
Dear Karthik.P
Thanks for your support.
BR
Johnny