Serial communications from Redundant RTUs

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Serial communications from Redundant RTUs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
22
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
12
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
michael_mckay_p
Crewman michael_mckay_p
Crewman

Posted: ‎2020-04-30 05:02 AM . Last Modified: ‎2023-05-30 10:13 PM

1 Like
1
660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-30 05:02 AM

Serial communications from Redundant RTUs

I would like to connect a daisy chain of 6 ModbusRTU devices on an RS-485 network to a pair of redundant Saitel DR HUe RTUs. As ModbusRTU is a master slave network is this possible? Will only one of the Saitel DRs attempt to control the RS-485 network at any one time? And so will the other take over if the primary fails?

 

Thanks for your thoughts

Labels
  • Labels:
  • Saitel range
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Iván_González
Lieutenant Iván_González Lieutenant
Lieutenant

Posted: ‎2020-05-02 09:02 AM

1 Like
0
651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-02 09:02 AM

Hi Michael,

 

Althoug redundancy in Saitel DR is a bit limited in comparison to Saitel DP, waht ou are proposing is certainly feasible. The Saitel redundancy mechanism is very robust and designed to manage syustems exactly as you  point at: HOT-STANDBY ssytems where only one CPU (the HOT one) is actively exchanging data with the field, while the STANDBY one gets database updates from it.

 

From an external point of view, if adequately configured, it is a single system both upstream and downstream.

See Answer In Context

Tags (2)
  • Tags:
  • redundancy
  • Saitel DR
Reply
Reply 1
Iván_González
Lieutenant Iván_González Lieutenant
Lieutenant

Posted: ‎2020-05-02 09:02 AM

1 Like
0
652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-02 09:02 AM

Hi Michael,

 

Althoug redundancy in Saitel DR is a bit limited in comparison to Saitel DP, waht ou are proposing is certainly feasible. The Saitel redundancy mechanism is very robust and designed to manage syustems exactly as you  point at: HOT-STANDBY ssytems where only one CPU (the HOT one) is actively exchanging data with the field, while the STANDBY one gets database updates from it.

 

From an external point of view, if adequately configured, it is a single system both upstream and downstream.

Tags (2)
  • Tags:
  • redundancy
  • Saitel DR
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of