New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Serial communications from Redundant RTUs
Protection & Control
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2020-04-3005:02 AM
Serial communications from Redundant RTUs
I would like to connect a daisy chain of 6 ModbusRTU devices on an RS-485 network to a pair of redundant Saitel DR HUe RTUs. As ModbusRTU is a master slave network is this possible? Will only one of the Saitel DRs attempt to control the RS-485 network at any one time? And so will the other take over if the primary fails?
Link copied. Please paste this link to share this article on your social media post.
2020-05-0209:02 AM
Hi Michael,
Althoug redundancy in Saitel DR is a bit limited in comparison to Saitel DP, waht ou are proposing is certainly feasible. The Saitel redundancy mechanism is very robust and designed to manage syustems exactly as you point at: HOT-STANDBY ssytems where only one CPU (the HOT one) is actively exchanging data with the field, while the STANDBY one gets database updates from it.
From an external point of view, if adequately configured, it is a single system both upstream and downstream.
Link copied. Please paste this link to share this article on your social media post.
2020-05-0209:02 AM
Hi Michael,
Althoug redundancy in Saitel DR is a bit limited in comparison to Saitel DP, waht ou are proposing is certainly feasible. The Saitel redundancy mechanism is very robust and designed to manage syustems exactly as you point at: HOT-STANDBY ssytems where only one CPU (the HOT one) is actively exchanging data with the field, while the STANDBY one gets database updates from it.
From an external point of view, if adequately configured, it is a single system both upstream and downstream.