Sepam S40 as baycontroller

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Sepam S40 as baycontroller
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
16
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
12
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
Anonymous user
Not applicable

Posted: ‎2021-09-21 02:26 PM

0 Likes
5
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 02:26 PM

Sepam S40 as baycontroller

Hello Experts!


I know this isn't a standard application, I am pretty sure this isn't recommended but my costumer need this.


I have a Sepam S40 protection Relay. This relay is control 3 CBs in one time. I disabled the circuit breaker control functions to use freely the I11 and I12.


The protection is controlled by Power Scada Operation with ModbusTCP. Now I want to operate the outputs by SCADA commands. From the Hungarian SE Support I got the information I can do this with the TC bits which is assigned to the V bits by Logical Equations.



My question is: How can I do this because I can't find the TC bits in the logical equations. Or if it’s impossible, where can I find documents to prove that it’s impossible?

 

 

Thanks you for your answers!

Labels
  • Labels:
  • Application cases
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndreMelo
Commander AndreMelo Commander
Commander

Posted: ‎2021-09-21 02:35 PM

0 Likes
0
855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 02:35 PM

Hi @Anonymous user,

 

Yes, you are right, unfortunately in the S40 series, we do not have Generic commands like the 80 series TC. They should be made a mixup with 80 series.

 

The unique way you can do it is by using a digital input to command the DJ.

 

It is a limitation of this model.

 

Best Regards

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
AndreMelo
Commander AndreMelo Commander
Commander

Posted: ‎2021-09-21 02:54 PM

0 Likes
3
853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 02:54 PM

Here is where you can prove it to your customer, all TC in 40 series are pre-defined functions and cannot be used as generic controls (page 172 of the attached manual)

 

 

TC sepam.PNG

See Answer In Context

Attachments
Tags (1)
  • Tags:
  • english
Reply
Replies 5
AndreMelo
Commander AndreMelo Commander
Commander

Posted: ‎2021-09-21 02:35 PM

0 Likes
0
856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 02:35 PM

Hi @Anonymous user,

 

Yes, you are right, unfortunately in the S40 series, we do not have Generic commands like the 80 series TC. They should be made a mixup with 80 series.

 

The unique way you can do it is by using a digital input to command the DJ.

 

It is a limitation of this model.

 

Best Regards

 

Tags (1)
  • Tags:
  • english
Reply
AndreMelo
Commander AndreMelo Commander
Commander

Posted: ‎2021-09-21 02:54 PM

0 Likes
3
854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 02:54 PM

Here is where you can prove it to your customer, all TC in 40 series are pre-defined functions and cannot be used as generic controls (page 172 of the attached manual)

 

 

TC sepam.PNG

Attachments
Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2021-09-22 11:05 AM

0 Likes
0
847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-22 11:05 AM

Thank you very much to your answer!

 

I forwarded this information to my customer.

Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2021-09-24 01:37 AM

0 Likes
1
838
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-24 01:37 AM

Just one more question @AndreMelo , with S80 protection is possible to do this application. If we change the S40 to S80 I will can access the TC bits in logical equation?

Tags (1)
  • Tags:
  • english
Reply
AndreMelo
Commander AndreMelo Commander
Commander

Posted: ‎2021-09-24 01:45 AM

0 Likes
0
836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-24 01:45 AM

Hi @Anonymous user ,

 

Yes, you can, with 80 series you can use the TC in both Ladder logic and Logic equation, just pay attention in the manual cause some TC has a pre-assigned function.

 

However, for this kind of application, I would prefer to use a P3 since it has pre-defined objects. But anyway, the answer is YES.

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of