Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Posted: 2021-09-21 02:26 PM
Link copied. Please paste this link to share this article on your social media post.
Hello Experts!
I know this isn't a standard application, I am pretty sure this isn't recommended but my costumer need this.
I have a Sepam S40 protection Relay. This relay is control 3 CBs in one time. I disabled the circuit breaker control functions to use freely the I11 and I12.
The protection is controlled by Power Scada Operation with ModbusTCP. Now I want to operate the outputs by SCADA commands. From the Hungarian SE Support I got the information I can do this with the TC bits which is assigned to the V bits by Logical Equations.
My question is: How can I do this because I can't find the TC bits in the logical equations. Or if it’s impossible, where can I find documents to prove that it’s impossible?
Thanks you for your answers!
Link copied. Please paste this link to share this article on your social media post.
Hi @Anonymous user,
Yes, you are right, unfortunately in the S40 series, we do not have Generic commands like the 80 series TC. They should be made a mixup with 80 series.
The unique way you can do it is by using a digital input to command the DJ.
It is a limitation of this model.
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Here is where you can prove it to your customer, all TC in 40 series are pre-defined functions and cannot be used as generic controls (page 172 of the attached manual)
Link copied. Please paste this link to share this article on your social media post.
Hi @Anonymous user,
Yes, you are right, unfortunately in the S40 series, we do not have Generic commands like the 80 series TC. They should be made a mixup with 80 series.
The unique way you can do it is by using a digital input to command the DJ.
It is a limitation of this model.
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Here is where you can prove it to your customer, all TC in 40 series are pre-defined functions and cannot be used as generic controls (page 172 of the attached manual)
Posted: 2021-09-22 11:05 AM
Link copied. Please paste this link to share this article on your social media post.
Thank you very much to your answer!
I forwarded this information to my customer.
Posted: 2021-09-24 01:37 AM
Link copied. Please paste this link to share this article on your social media post.
Just one more question @AndreMelo , with S80 protection is possible to do this application. If we change the S40 to S80 I will can access the TC bits in logical equation?
Link copied. Please paste this link to share this article on your social media post.
Hi @Anonymous user ,
Yes, you can, with 80 series you can use the TC in both Ladder logic and Logic equation, just pay attention in the manual cause some TC has a pre-assigned function.
However, for this kind of application, I would prefer to use a P3 since it has pre-defined objects. But anyway, the answer is YES.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.