Hello Experts!
I know this isn't a standard application, I am pretty sure this isn't recommended but my costumer need this.
I have a Sepam S40 protection Relay. This relay is control 3 CBs in one time. I disabled the circuit breaker control functions to use freely the I11 and I12.
The protection is controlled by Power Scada Operation with ModbusTCP. Now I want to operate the outputs by SCADA commands. From the Hungarian SE Support I got the information I can do this with the TC bits which is assigned to the V bits by Logical Equations.
My question is: How can I do this because I can't find the TC bits in the logical equations. Or if it’s impossible, where can I find documents to prove that it’s impossible?
Thanks you for your answers!
Link copied. Please paste this link to share this article on your social media post.
Hi @Anonymous user,
Yes, you are right, unfortunately in the S40 series, we do not have Generic commands like the 80 series TC. They should be made a mixup with 80 series.
The unique way you can do it is by using a digital input to command the DJ.
It is a limitation of this model.
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Here is where you can prove it to your customer, all TC in 40 series are pre-defined functions and cannot be used as generic controls (page 172 of the attached manual)
Link copied. Please paste this link to share this article on your social media post.
Hi @Anonymous user,
Yes, you are right, unfortunately in the S40 series, we do not have Generic commands like the 80 series TC. They should be made a mixup with 80 series.
The unique way you can do it is by using a digital input to command the DJ.
It is a limitation of this model.
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Here is where you can prove it to your customer, all TC in 40 series are pre-defined functions and cannot be used as generic controls (page 172 of the attached manual)
Posted: 2021-09-22 11:05 AM
Link copied. Please paste this link to share this article on your social media post.
Thank you very much to your answer!
I forwarded this information to my customer.
Posted: 2021-09-24 01:37 AM
Link copied. Please paste this link to share this article on your social media post.
Just one more question @AndreMelo , with S80 protection is possible to do this application. If we change the S40 to S80 I will can access the TC bits in logical equation?
Link copied. Please paste this link to share this article on your social media post.
Hi @Anonymous user ,
Yes, you can, with 80 series you can use the TC in both Ladder logic and Logic equation, just pay attention in the manual cause some TC has a pre-assigned function.
However, for this kind of application, I would prefer to use a P3 since it has pre-defined objects. But anyway, the answer is YES.