Hello @Ahmedmenaze
The error code 0x8C0F0000 is related to the main sampling buffer. This maintenance occurs if the buffer becomes full.
Yes, you can reboot the relay by switching off and on the power supply and recover it The relay must be repaired if the error persists or if it occurs again and again.
Link copied. Please paste this link to share this article on your social media post.
Hello @Ahmedmenaze
The error code 0x8C0F0000 is related to the main sampling buffer. This maintenance occurs if the buffer becomes full.
Yes, you can reboot the relay by switching off and on the power supply and recover it The relay must be repaired if the error persists or if it occurs again and again.