Dear All,
Is there a procedure of pairing PowerLogic P5F30 with new hardware B with firmware V02.501 + REL51044 with one sensor CL110.
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa197124_brid,
Please find one part of user manual attached which includes the sensor pairing in chapter 'Pairing of sensors', the process is described in detailed I think. Please let me know if you have more questions.
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa197124_brid,
Please find one part of user manual attached which includes the sensor pairing in chapter 'Pairing of sensors', the process is described in detailed I think. Please let me know if you have more questions.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Could I confirm if the sensors can be re-allocated from P5 to another P5 simply by copying its RFID inside the configuration file ? similar to the old ZBRN where you could copy its line of code inside the csv file..
Link copied. Please paste this link to share this article on your social media post.
Hello @wasabi,
No, simply copying RFID can not restore the Zigbee connection from P5 A to P5 B. Please refer to P5 user manual and search "PowerLogic P5 is replaced" for the detailed solution.
Link copied. Please paste this link to share this article on your social media post.
Hello @Igormugnos,
Is the issue solved? If not, can you provide more details? Which operation did you do prior to this abnormal status?
Link copied. Please paste this link to share this article on your social media post.
Hi!
It was solved in another topic that i've opened here.
thanks
Link copied. Please paste this link to share this article on your social media post.
Hi,
I just have 1 more question regarding the module REL51044, this is labeled as EXR and its got a RJ45 port, may i know what they are used for ? if the P5 already have comms via another module then what is this RJ45 for ? is it modbus TCP ? thanks
Link copied. Please paste this link to share this article on your social media post.
Hello @wasabi,
Please refer to description from manual as below. The RJ45 on EXR is not used for Modbus TCP/DNP3 TCP/IEC61850/etc, but IRIG-B/CLIO/RTD/ZigBee communication.