P3T32 Utilize for Cable Differential

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • P3T32 Utilize for Cable Differential
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
32
Arun-kumar_PS
Commander Arun-kumar_PS Commander
16
HenriGRASSET
Captain HenriGRASSET Captain
15
View All
Related Products
product field
PowerLogic
PowerLogic P2

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Vasutha
Ensign Vasutha Ensign
Ensign

Posted: ‎2024-04-11 01:01 AM

0 Likes
3
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-11 01:01 AM

P3T32 Utilize for Cable Differential

Hi Team, we have got the challenge from Customer to utilize P3T32 - 87T for cable differential protection for bus-tie feeder.

 

I understand that, in the principle of differential protection, it's able to apply but I'm not sure about protection relay setting and parameter configuration concerned.

 

Could you please advise whether it is possible to apply P3T32?

 

Vasutha_0-1712821810567.png

 

  • Thumbnail of PowerLogic P2
    PowerLogic
    PowerLogic P2
View products (1)
Labels
  • Labels:
  • PowerLogic P3
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Rudolf_Simon
Commander Rudolf_Simon Commander
Commander

Posted: ‎2024-04-12 12:26 AM

1 Like
2
1321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-12 12:26 AM

Hello Vasutha,

you're correct, differential protection in principle can be applied, also a "transformer differntial" like P3T32, if the distance between IED and CTs at cable ends can be managed by CT sizing (mainly by cross section of wires).
In such application (like in generator protection) no transformer specific settings apply:

  • Set vector group = Yy0
  • No zero-sequence current elimination
  • Same nominal voltage on both sides
  • Nominal power should reflect rated (or maximum) load current of the protected cable (e.g. for max. load current = 100 A and nominal voltage 10 kV, I would set nominal power = (100 A * 10 kV * sqrt(3) = 1 732 kVA) => 2000 kVA

These P3T32 settings are in GENERAL/Scaling: Rudolf_Simon_0-1712906357550.png

 

regards

Rudolf

 

See Answer In Context

Reply
Replies 3
Rudolf_Simon
Commander Rudolf_Simon Commander
Commander

Posted: ‎2024-04-12 12:26 AM

1 Like
2
1322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-12 12:26 AM

Hello Vasutha,

you're correct, differential protection in principle can be applied, also a "transformer differntial" like P3T32, if the distance between IED and CTs at cable ends can be managed by CT sizing (mainly by cross section of wires).
In such application (like in generator protection) no transformer specific settings apply:

  • Set vector group = Yy0
  • No zero-sequence current elimination
  • Same nominal voltage on both sides
  • Nominal power should reflect rated (or maximum) load current of the protected cable (e.g. for max. load current = 100 A and nominal voltage 10 kV, I would set nominal power = (100 A * 10 kV * sqrt(3) = 1 732 kVA) => 2000 kVA

These P3T32 settings are in GENERAL/Scaling: Rudolf_Simon_0-1712906357550.png

 

regards

Rudolf

 

Reply
Vasutha
Ensign Vasutha Ensign
Ensign

Posted: ‎2024-04-16 10:59 PM . Last Modified: ‎2024-04-16 11:00 PM

0 Likes
1
1278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-16 10:59 PM

Hello Rudolf,

Thank you for your reply and advice. I would like to ask for detail setting about "power direction (outgoing or incoming)" in Easergy Pro.

Because, actually, the power will be both direction which is depended on Incoming A or B and bus-tie closing. 

Vasutha_0-1713333607502.png

 

Reply
Rudolf_Simon
Commander Rudolf_Simon Commander
Commander

Posted: ‎2024-04-26 12:32 AM

1 Like
0
1241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-26 12:32 AM

Hello Vasutha,
this 'power direction' setting defines, in which direction measured power is with positive sign.
So, 'outgoing' means power flowing from the bus to the feeder is with positive sign, power flowing from the feeder to the bus with negative sign. That's all.
It does not affect protection functions. 

regards

Rudolf

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore