P3T32 Utilize for Cable Differential
Protection & Control
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
  • EcoStruxure Power & Grid
  • Protection & Control
  • Re: P3T32 Utilize for Cable Differential
Araceli_Monje
Araceli_Monje Mentor
74
JuanRayo
JuanRayo Mentor
39
Arun-kumar_PS
Arun-kumar_PS Mentor
33
Back to Protection & Control
Vasutha
Vasutha Explorer
Explorer
Posted: ‎2024-04-11 01:01 AM
1885
Hi Team, we have got the challenge from Customer to utilize P3T32 - 87T for cable differential protection for bus-tie feeder.
I understand that, in the principle of differential protection, it's able to apply but I'm not sure about protection relay setting and parameter configuration concerned.
Could you please advise whether it is possible to apply P3T32?
  • Thumbnail of PowerLogic P2
    PowerLogic
    PowerLogic P2
View products (1)
  • PowerLogic P3
Rudolf_Simon
Rudolf_Simon Leader
Leader
Posted: ‎2024-04-12 12:26 AM
2
1851
Hello Vasutha,
you're correct, differential protection in principle can be applied, also a "transformer differntial" like P3T32, if the distance between IED and CTs at cable ends can be managed by CT sizing (mainly by cross section of wires).
In such application (like in generator protection) no transformer specific settings apply:
  • Set vector group = Yy0
  • No zero-sequence current elimination
  • Same nominal voltage on both sides
  • Nominal power should reflect rated (or maximum) load current of the protected cable (e.g. for max. load current = 100 A and nominal voltage 10 kV, I would set nominal power = (100 A * 10 kV * sqrt(3) = 1 732 kVA) => 2000 kVA
These P3T32 settings are in GENERAL/Scaling: Rudolf_Simon_0-1712906357550.png
regards
Rudolf
Replies 3
Rudolf_Simon
Rudolf_Simon Leader
Leader
2
1852
Hello Vasutha,
regards
Rudolf
Vasutha
Vasutha Explorer
Explorer
Posted: ‎2024-04-16 10:59 PM . Last Modified: ‎2024-04-16 11:00 PM
1808
Hello Rudolf,
Thank you for your reply and advice. I would like to ask for detail setting about "power direction (outgoing or incoming)" in Easergy Pro.
Because, actually, the power will be both direction which is depended on Incoming A or B and bus-tie closing.
Rudolf_Simon
Rudolf_Simon Leader
Leader
Posted: ‎2024-04-26 12:32 AM
Hello Vasutha,
this 'power direction' setting defines, in which direction measured power is with positive sign.
So, 'outgoing' means power flowing from the bus to the feeder is with positive sign, power flowing from the feeder to the bus with negative sign. That's all.
It does not affect protection functions.
regards
Rudolf