MicroLogic 6.0 X erroneous trips

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • MicroLogic 6.0 X erroneous trips
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
28
HenriGRASSET
Captain HenriGRASSET Captain
15
Arun-kumar_PS
Commander Arun-kumar_PS Commander
14
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
Jonathan_H1
Jonathan_H1
Cadet

Posted: ‎2025-06-13 08:02 AM . Last Modified: ‎2025-06-13 11:40 AM

0 Likes
1
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-13 08:02 AM

MicroLogic 6.0 X erroneous trips

We have a Micrologic 6.0 X in a MTZ2-32H3 3200 amps. This is a 480V CAT rental generator.  We had a customer that was getting erroneous ground fault trips every 3 to 4 closures of the breaker. They were stepping up 12kv with about 1.8mega watt bulk load. This machine was trying to be used at a hospital unfortunately we had to send another unit. Going through the settings every thing is turn up to the maxes and it was still happening.

Is there anything that can be done?

 

Also is there a way to testthe ground fault safely on 3ph

 

 

Labels
  • Labels:
  • Application cases
  • Training
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
Lt. Commander

Posted: ‎2025-07-29 08:24 AM . Last Modified: ‎2025-07-29 08:25 AM

0 Likes
0
96
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-29 08:24 AM

Dear @Jonathan_H1 , Micrologic is not inside the portfolio managed in this Protection & Control Forum, my apologies. I would suggest you to post your question in the Power Distribution Forum, our colleagues there may be able to support you or connect you with the right people that are able to help you with your question , Power Distribution and Digital Support - Schneider Electric Community

See Answer In Context

Reply
Reply 1
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
Lt. Commander

Posted: ‎2025-07-29 08:24 AM . Last Modified: ‎2025-07-29 08:25 AM

0 Likes
0
97
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-29 08:24 AM

Dear @Jonathan_H1 , Micrologic is not inside the portfolio managed in this Protection & Control Forum, my apologies. I would suggest you to post your question in the Power Distribution Forum, our colleagues there may be able to support you or connect you with the right people that are able to help you with your question , Power Distribution and Digital Support - Schneider Electric Community

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of