Hello @devalkansagara-24
This alarm is raised when the P122 relay self-diagnosis function identifies a fault in the auxiliary power supply rails internal to the relay. This fault is classified as a major alarm and the relay cannot perform protection & automation functions . The relay must be repaired to rectify and reset the alarm. Please remove the relay from use and contact the local Schneider office for repair support.
Link copied. Please paste this link to share this article on your social media post.
Hello @devalkansagara-24
This alarm is raised when the P122 relay self-diagnosis function identifies a fault in the auxiliary power supply rails internal to the relay. This fault is classified as a major alarm and the relay cannot perform protection & automation functions . The relay must be repaired to rectify and reset the alarm. Please remove the relay from use and contact the local Schneider office for repair support.