Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Ferroresonance in isolated 6 kV network

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Ferroresonance in isolated 6 kV network
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Araceli_Monje Mentor
60
Arun-kumar_PS
Arun-kumar_PS Mentor
26
JuanRayo
JuanRayo Mentor
24
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-06-09 03:08 AM

0 Likes
2
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-09 03:08 AM

Ferroresonance in isolated 6 kV network

Dear collegues,

 

Our client has a problem with ferroresonance in isolated 6 kV network. In some cases, when earth-fault occurs, after isolation of faulty line, in voltage transformers voltage of 25 Hz is induced and after some time explosion of voltage transformers happen. They tried to solve this problem by installation of resistor in the open delta winding of voltage transformers, but problem continue to happen even after that. Now they asked us to try to solve this problem by using relay protection.


Does anyone have an idea how to solve this problem using Schneider Electric protection relays? Also any other idea will be helpful.


I will be very thankful if anyone can help with this problem.

Labels
  • Labels:
  • Application cases
Tags (4)
  • Tags:
  • earth-fault
  • ferroresonance
  • isolated network
  • relay protection
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ian_Young
Ian_Young Mentor
Mentor

Posted: ‎2020-06-09 04:00 PM

0 Likes
1
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-09 04:00 PM

Hi Marko,

 

Cahier technique n° 190 is a very good document on the topic of ferroresonance. 

 

https://www.se.com/us/en/download/document/ECT190/ 

 

As this document states to have classical ferroresonance you need

  • simultaneous presence of capacitances with non-linear inductances,
  • existence in the system of at least one point whose potential is not fixed (isolated neutral, single fuse blowing, single phase switching....),
  • lightly loaded system components (unloaded power or instrument voltage transformers...) or low short-circuit power sources (generators).

So it is best to understand where these are coming from. It sounds like when the faulty line is tripped they are disconnecting from the system earth and the VT becomes the earth for an isolated system. If the system is isolated even briefly then the VT needs to be rated accordingly.

 

We find similar situations occurring at data centres during transition to local supply. What is the application in this case?

Ian YOUNG
CoE member, L3 support, P7 product architect

See Answer In Context

Reply
Replies 2
Ian_Young
Ian_Young Mentor
Mentor

Posted: ‎2020-06-09 04:00 PM

0 Likes
1
1261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-09 04:00 PM

Hi Marko,

 

Cahier technique n° 190 is a very good document on the topic of ferroresonance. 

 

https://www.se.com/us/en/download/document/ECT190/ 

 

As this document states to have classical ferroresonance you need

  • simultaneous presence of capacitances with non-linear inductances,
  • existence in the system of at least one point whose potential is not fixed (isolated neutral, single fuse blowing, single phase switching....),
  • lightly loaded system components (unloaded power or instrument voltage transformers...) or low short-circuit power sources (generators).

So it is best to understand where these are coming from. It sounds like when the faulty line is tripped they are disconnecting from the system earth and the VT becomes the earth for an isolated system. If the system is isolated even briefly then the VT needs to be rated accordingly.

 

We find similar situations occurring at data centres during transition to local supply. What is the application in this case?

Ian YOUNG
CoE member, L3 support, P7 product architect
Reply
Anonymous user
Not applicable

Posted: ‎2020-06-09 11:38 PM

0 Likes
0
1253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-09 11:38 PM

The application in this case is mine of coal.

 

Thank you very much for answer.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore