EasyLogic T150 (formerly Saitel DR) - Issue with IEC 61850 ICD file from ABB protection relay

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • EasyLogic T150 (formerly Saitel DR) - Issue with IEC 61850 ICD file from ABB protection relay
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Protection & Control
Start a Topic
Lanos
Crewman Lanos
Crewman

Posted: ‎2025-12-04 06:34 AM . Last Modified: ‎2025-12-16 01:49 AM

0 Likes
3
223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-04 06:34 AM

EasyLogic T150 (formerly Saitel DR) - Issue with IEC 61850 ICD file from ABB protection relay

Hi,

I am experiencing an issue with my IEC 61850 configuration on the RTU. I imported ICD files from an ABB relay into the Easergy Builder application, but when I send the configuration to the Saitel DR RTU, I receive a Data Mismatch error.

The protection and digital signals are coming through correctly, but the analogue data is causing the mismatch.

Below are the diagnostics I receive when sending the configuration that includes the analogue data tags.

 

Screenshot 2025-12-04 160251.png

Screenshot 2025-12-04 160154.png

Screenshot 2025-12-04 160251.png

Please assist.

i do not get these errors when I only have the Protection and Digitals.

Labels
  • Labels:
  • IEC61850
  • Saitel range
  • Smart Design & Engineering
Tags (5)
  • Tags:
  • EasyLogic T150
  • english
  • iec 61850
  • Saitel DR
  • T150
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
SESA219022
SESA219022 Cadet
Cadet

Posted: ‎2025-12-05 05:19 AM

0 Likes
1
189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-05 05:19 AM

Hello Lanos,

I think the problem is that the IED does not have the dataset in the same order as your imported CID.

What I would do is use IEDScout or IEDExplore to see what the IED has loaded.

Best regards

Reply
Lanos
Crewman Lanos
Crewman

Posted: ‎2025-12-08 12:05 AM

0 Likes
0
126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-08 12:05 AM

hallo,

I did use IEDExplore and the datasets match. The problem is just with the analogues.

kind regards

Reply
JuanRayo
Lt. Commander JuanRayo Lt. Commander
Lt. Commander

Posted: ‎2025-12-09 12:55 AM

0 Likes
0
102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-09 12:55 AM

Hello . I think @SESA219022  is correct but to determine the exact point where the problem occurs I need you to share with us the configuration used and wireshark traces captured after a disconnection with the IED¨s affected.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore