Hi,
I am experiencing an issue with my IEC 61850 configuration on the RTU. I imported ICD files from an ABB relay into the Easergy Builder application, but when I send the configuration to the Saitel DR RTU, I receive a Data Mismatch error.
The protection and digital signals are coming through correctly, but the analogue data is causing the mismatch.
Below are the diagnostics I receive when sending the configuration that includes the analogue data tags.
Please assist.
i do not get these errors when I only have the Protection and Digitals.
Link copied. Please paste this link to share this article on your social media post.
Hello Lanos,
I think the problem is that the IED does not have the dataset in the same order as your imported CID.
What I would do is use IEDScout or IEDExplore to see what the IED has loaded.
Best regards
Link copied. Please paste this link to share this article on your social media post.
hallo,
I did use IEDExplore and the datasets match. The problem is just with the analogues.
kind regards
Link copied. Please paste this link to share this article on your social media post.
Hello . I think @SESA219022 is correct but to determine the exact point where the problem occurs I need you to share with us the configuration used and wireshark traces captured after a disconnection with the IED¨s affected.