Easergy P3L30 line differential issue

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Easergy P3L30 line differential issue
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
16
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
12
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
Milica_Repac
Lieutenant JG Milica_Repac
Lieutenant JG

Posted: ‎2020-05-21 07:00 AM . Last Modified: ‎2023-05-30 10:00 PM

0 Likes
1
748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-21 07:00 AM

Easergy P3L30 line differential issue

According to user manual documentation for Easergy P3L30 estimated transmission length for line differential protection is 15km. We need to protect transmission line, which is 40km long. Is it possible to extend this length? Is there any additional device, which can be used with Easergy P3L30 to extend this length? 

 

We have considered MiCOM line differrential relays, but they don't meet other requirements. 

 

I'll be grateful for any suggestions.

Labels
  • Labels:
  • Application cases
Tags (2)
  • Tags:
  • Easergy P3L30
  • Line differential
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
HenriGRASSET
Captain HenriGRASSET Captain
Captain

Posted: ‎2020-06-02 12:26 AM

0 Likes
0
725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-02 12:26 AM

Hello,

 

From the P3L user manual available in our website, you can find that the maximum length is 120 km with the list of accessories in clause 13.2. Accessories - Table 172 - Easergy P3L30 accessories

 

 

EDISON Expert

See Answer In Context

Reply
Reply 1
HenriGRASSET
Captain HenriGRASSET Captain
Captain

Posted: ‎2020-06-02 12:26 AM

0 Likes
0
726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-02 12:26 AM

Hello,

 

From the P3L user manual available in our website, you can find that the maximum length is 120 km with the list of accessories in clause 13.2. Accessories - Table 172 - Easergy P3L30 accessories

 

 

EDISON Expert
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of