According to the Easergy P3 catalog, the P3F30 model does not support ANSI 64REF (Low impedance). I need to confirm if it supports this function based on high impedance criteria.
Thanks in advance.
  • Thumbnail of PowerLogic P2
    PowerLogic
    PowerLogic P2
View products (1)
  • PowerLogic P3
Gregory_Meunier
Lt. Commander Gregory_Meunier Lt. Commander
Lt. Commander
Posted: ‎2024-07-16 10:47 AM
1621
Normally any overcurrent relay can perform an high impedance protection, then the issue is that there are not always guidance for the CT sizing provided with the User manual.
For Easergy P3, the guidance can be found in a separate application, appended in that post.
Gregory_Meunier
Lt. Commander
1622
Jaeyoung-Seong
Jaeyoung-Seong
Cadet
Posted: ‎2024-07-16 05:20 PM
Thank you for your response. I will refer to the provided materials.