Dear Colleagues! We have a P3U30 relay, config: P3U30-7CBA1CCAA. We have selected the LPVT input, but in the protection function the Overvoltage (ANSI 59) and Undervoltage (ANSI 27) does not appear. Could somebody advise to us some solution? Thanks in advance!
Labels
- Labels:
-
PowerLogic P3
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
2023-12-19
11:51 PM
This is a known issue and have been fixed on version v30.207. Propose to use the latest Easergy pro V4.5.0 to create EPZ file of version v30.207 offline.