CT mismatch in differential protection MiCOM P54x

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • CT mismatch in differential protection MiCOM P54x
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
22
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
Aescobar
Aescobar
Cadet

Posted: ‎2024-05-13 07:09 AM

0 Likes
1
1989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-13 07:09 AM

CT mismatch in differential protection MiCOM P54x

Hello community,

 

I would like to confirm how the differential protection works on the MiCOM P54x relays in the case of different CT ratios. In the following example, end Ahas a 1400/1 CT ratio and end B has a 2500/1 ratio. 

Aescobar_1-1715608680680.png

 

The manual recommends that the parameter   Ph Ct Corr'tion should be calculated with primary rated current of the smallest CT ratio as a base current:

Ph Ct Corr'tion=CT local/CTmin.

 

So in this case, should be:

End A: Ph Ct Corr'tion=1400A/1400A=1.00

End B: Ph Ct Corr'tion=2500A/1400A= 1.790

 

With this configuration, it is okay to set the rest of the differential settings (Phase Is1, Phase Is2 and Phase Is1 CTS) on the same secondary values in both ends of the line?

 

Looking forward to your reply!

Thank you.

 

 

 

Labels
  • Labels:
  • Application cases
  • PowerLogic P5
Tags (3)
  • Tags:
  • differential protection
  • english
  • MiCOM P54x
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Gregory_Meunier
Lt. Commander Gregory_Meunier Lt. Commander
Lt. Commander

Posted: ‎2024-05-14 05:35 PM . Last Modified: ‎2024-07-09 04:01 PM

1 Like
0
1967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-14 05:35 PM

Hello,

 

The line differential protection does its internal calculation in per-unit ; consistent per-unit definition must be set at each end.

This means

- For line or cable, the same per-unit values ar each end correspond to the same primary current.

- For transformer in zone application, the same per-unit definition must match the per-unit base of transformer winding.

 

I only consider the example of the line or application without transformer.

 

By default, 1 pu corresponds to 1 A for 1 A inputs or 5 A for 5 A inputs.

We can extend the reasoning with the CT primary current rating but ultimately the relay is measuring secondary currents.

If the CT ratios are different at either end, there is no longer one common per-unit definition but two definitions that will cause the relay to trip.

 

Ph CT Correction parameter is set to adjust the per-unit definition.

Then 1 pu corresponds to 1 A / Ph CT Correction in 1 A inputs or 5 A / Ph CT Correction in 5 A inputs.

 

Is1, Is2 and Is1 CTS are converted in pu without taking into account the Ph CT Correction.

With 1A rated secondary current, 0.2 A means 0.2 pu.

 

Example without Phase CT Correction

The line is loaded with 1000 A.

- End A: 1400/1

             Iload(sec) = 1000 A / 1400 A × 1 A = 0.71 A

             Is1 = 0.2 pu => 0.2 A(sec) or 280 A(prim)

             1 pu => 1 A(sec) or 1400 A(prim)

              => Ilocalpu = 0.71 A / 1 A = 0.71 pu

- End B: 2500/1

             Iload(sec) = 1000 A / 2500 A × 1 A = 0.4 A

             Is1 = 0.2 pu => 0.2 A(sec) or 500 A(prim)

             1 pu => 1 A(sec) or 2500 A(prim)

              => Ilocalpu = 0.4 A / 1 A = 0.4 pu

Idiff => 0.71 pu - 0.4 pu  = 0.31 pu

The differential current is due the inconsistency of the pu definition on the both ends, the relay malfunctions by diff trip.

 

Example with Phase CT Correction

The line is loaded with 1000 A.

- End A: 1400/1 & Ph CT Correction = 1

             1 pu => 1 A(sec) or 1400 A(prim)

             Iload(sec) = 1000 A / 1400 A × 1 A = 0.71 A

              /!\ Is1 set at  0.2 A(sec) - 280 A(prim) => 0.2 pu => Actual threshold at 0.2 A(sec) - 280 A(prim)

              => Ilocalpu = 0.71 A / 1 A = 0.714 pu

- End B: 2500/1 & Ph CT Correction = 2500/1400 = 1.79

             1 pu => 0.559 A(sec) or 1397 A(prim) (same as End A)

             Iload(sec) = 1000 A / 2500 A × 1 A = 0.4 A

             /!\ Is1 set at  0.2 A(sec) - 500A (prim) => 0.2 pu => Actual threshold at 0.112 A(sec) - 280 A(prim)

              => Ilocalpu = Ilocalpu = 0.4 A / (1 A / Ph CT Correction ) = 0.716 pu

Idiff => 0.716 pu - 0.714 pu = 0.02 pu (mismatch due to rounding error)

Consistent pu definition on both ends, no malfunction.

 

Regarding Is1, Is2 it is recommended to apply the same primary values because the calculated differential and bias currents are the same at all ends.

For Is1 CTS, the same applies, however in the case of three-end line we should consider that the normal load current at all ends which are not the same.

See Answer In Context

Reply
Reply 1
Gregory_Meunier
Lt. Commander Gregory_Meunier Lt. Commander
Lt. Commander

Posted: ‎2024-05-14 05:35 PM . Last Modified: ‎2024-07-09 04:01 PM

1 Like
0
1968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-14 05:35 PM

Hello,

 

The line differential protection does its internal calculation in per-unit ; consistent per-unit definition must be set at each end.

This means

- For line or cable, the same per-unit values ar each end correspond to the same primary current.

- For transformer in zone application, the same per-unit definition must match the per-unit base of transformer winding.

 

I only consider the example of the line or application without transformer.

 

By default, 1 pu corresponds to 1 A for 1 A inputs or 5 A for 5 A inputs.

We can extend the reasoning with the CT primary current rating but ultimately the relay is measuring secondary currents.

If the CT ratios are different at either end, there is no longer one common per-unit definition but two definitions that will cause the relay to trip.

 

Ph CT Correction parameter is set to adjust the per-unit definition.

Then 1 pu corresponds to 1 A / Ph CT Correction in 1 A inputs or 5 A / Ph CT Correction in 5 A inputs.

 

Is1, Is2 and Is1 CTS are converted in pu without taking into account the Ph CT Correction.

With 1A rated secondary current, 0.2 A means 0.2 pu.

 

Example without Phase CT Correction

The line is loaded with 1000 A.

- End A: 1400/1

             Iload(sec) = 1000 A / 1400 A × 1 A = 0.71 A

             Is1 = 0.2 pu => 0.2 A(sec) or 280 A(prim)

             1 pu => 1 A(sec) or 1400 A(prim)

              => Ilocalpu = 0.71 A / 1 A = 0.71 pu

- End B: 2500/1

             Iload(sec) = 1000 A / 2500 A × 1 A = 0.4 A

             Is1 = 0.2 pu => 0.2 A(sec) or 500 A(prim)

             1 pu => 1 A(sec) or 2500 A(prim)

              => Ilocalpu = 0.4 A / 1 A = 0.4 pu

Idiff => 0.71 pu - 0.4 pu  = 0.31 pu

The differential current is due the inconsistency of the pu definition on the both ends, the relay malfunctions by diff trip.

 

Example with Phase CT Correction

The line is loaded with 1000 A.

- End A: 1400/1 & Ph CT Correction = 1

             1 pu => 1 A(sec) or 1400 A(prim)

             Iload(sec) = 1000 A / 1400 A × 1 A = 0.71 A

              /!\ Is1 set at  0.2 A(sec) - 280 A(prim) => 0.2 pu => Actual threshold at 0.2 A(sec) - 280 A(prim)

              => Ilocalpu = 0.71 A / 1 A = 0.714 pu

- End B: 2500/1 & Ph CT Correction = 2500/1400 = 1.79

             1 pu => 0.559 A(sec) or 1397 A(prim) (same as End A)

             Iload(sec) = 1000 A / 2500 A × 1 A = 0.4 A

             /!\ Is1 set at  0.2 A(sec) - 500A (prim) => 0.2 pu => Actual threshold at 0.112 A(sec) - 280 A(prim)

              => Ilocalpu = Ilocalpu = 0.4 A / (1 A / Ph CT Correction ) = 0.716 pu

Idiff => 0.716 pu - 0.714 pu = 0.02 pu (mismatch due to rounding error)

Consistent pu definition on both ends, no malfunction.

 

Regarding Is1, Is2 it is recommended to apply the same primary values because the calculated differential and bias currents are the same at all ends.

For Is1 CTS, the same applies, however in the case of three-end line we should consider that the normal load current at all ends which are not the same.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of