internal arc withstand

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • internal arc withstand
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
66
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
rakeshNag123
Crewman rakeshNag123 Crewman
Crewman

Posted: ‎2020-10-22 12:09 PM . Last Modified: ‎2021-10-28 01:17 AM

0 Likes
6
6763
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-22 12:09 PM . Last Modified: ‎2021-10-28 01:17 AM

internal arc withstand

Can we specify an internal arc withstand value of say for example 85 KA for 0.4 sec while the short circuit withstand specified for the assembly is 50 KA for 1 second . I assume yes we can if not can someone explain why not ?

Labels
  • Labels:
  • Safety - People Safety
  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
PascalL
Lt. Commander PascalL Lt. Commander
Lt. Commander

Posted: ‎2020-10-27 08:41 AM

In response to rakeshNag123
1 Like
1
6728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-27 08:41 AM

Hi Rakesh,

 

Regarding your reply: "i may specify  is 50 KA /0.4 or 50 KA/0.3 (if prospective maximum short circuit is 50 KA /1s)but for building up a safety margin i can specify 65 KA/.5 or 85 KA/0.4 or 100 KA/0.4 . And i may give reasoning to the customer that higher the internal arc withstand of a panel more safer is the panel ( irrespective of the maximum prospective  short circuit current). Am i right here ?"

Yes you are right Rakesh.

 

About the second part of your reply: "under what circumstances can a current of 65 KA , 85 KA or 100 KA might flow in the system when maximum prospective short circuit current is 50 KA only ? "

If the Icc is 50KA you have no chance to have 65 or 85 or even 100KA.

If I make a parallels explanation...suppose you buy a car. The car is able to run at 190km/h. The speed is limited at 130km/h on the highway. So do you have any chance to exceed 130km/h? No but it is comfortable, the result is when you drive the noise will be lower, the reliability higher, the safety also.

To an assembly it is the same thing. Probably in case of internal arc the impact into the assembly will be less important, probably the MTTR(mind time to repair) will be better...we call that a safety margin.

Who can do more, can do less 🙂

Best regards,

PascalL.

See Answer In Context

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 6
PascalL
Lt. Commander PascalL Lt. Commander
Lt. Commander

Posted: ‎2020-10-23 07:10 AM

1 Like
5
6753
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-23 07:10 AM

The short-circuit withstand indicated in your example 50KA/1s is linked to the maximum short-circuit of the main supply generally corresponding to the Icc of the MV/LV transformer.

If you want to specify an internal arc performance, you can specify:

  • IP arc minimum 50KA/1s ; assumption the internal arc isn’t interrupted by any SCPD (short-circuit protective device)
  • IPc arc 50KA, assumption the internal arc is interrupted by a SCPD

This specification need to be referred to the IEC TR 61641 and the assembly shall be tested according to this TR.

In your example 50KA/1s, the assembly Prisma from Schneider-Electric has been tested to IPc arc 50KA and so in accordance to the requirement.

The assembly OKKEN from Schneider-Electric has been tested to IP arc 100KA/1s and so in accordance and exceeding to the requirement.

Hoping this answer will help you, with my best regards,

 

Pascal LEPRETRE

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

rakeshNag123
Crewman rakeshNag123 Crewman
Crewman

Posted: ‎2020-10-23 08:19 AM

In response to PascalL
0 Likes
4
6750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-23 08:19 AM

Thank you pascal !

 

I am still not very clear . I would want to reposition my query in this manner .

 

Suppose I am a specifier . I have  designed a system where maximum short circuit possible is 50 KA and I mention in the specification that the LV assembly shall have a short circuit withstand capacity of 50 KA / 1sec . Now I wish to ensure that the LV assembly shall  also be internal arc tested as per IEC /TR 61641 . So I go ahead and I mention in the specification that LV assembly shall be internal arc tested as per IEC/TR 61641 for a value of 85KA/0.4 sec or 100 KA/0.3 sec .

 

Meaning when system short circuit level is 50 KA can I demand my assembly to have a internal arc withstand of 85 KA/0. 4 sec or 100 KA /0.3 sec . Is this a logical spec in ?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

PascalL
Lt. Commander PascalL Lt. Commander
Lt. Commander

Posted: ‎2020-10-26 03:00 AM

In response to rakeshNag123
1 Like
3
6736
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-26 03:00 AM

I  try to be more precise,

Regarding the level of short-circuit, as you said the maximum prospective short-circuit is 50KA. So, using your wording it is not logical to require an internal arc withstand exceeding this value but it will propose a safety margin.

About the duration now, you can specify a duration of 0,3s or 0,4s in that situation you need to be sure the time delay of the Incomer (if there is one) don’t exceed this time.

You minimum specification could be  for internal-arc 50 KA/0,4s or 50 KA/0,3s and if you want a have a safety margin to that performance also 85 or 100 KA/0,4s

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

rakeshNag123
Crewman rakeshNag123 Crewman
Crewman

Posted: ‎2020-10-26 09:12 PM

In response to PascalL
0 Likes
2
6733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-26 09:12 PM

Hi pascal ,

 

Thank you for your explanation. I must admit you have addressed my query precisely . In order to  assure myself that i have understood , wish to take your final opinion again along with an additional query . 

 

You have mentioned in your response below  "You minimum specification could be  for internal-arc 50 KA/0,4s or 50 KA/0,3s and if you want a have a safety margin to that performance also 85 or 100 KA/0,4s"

 

so , this means minimum i may specify  is 50 KA /0.4 or 50 KA/0.3 (if prospective maximum short circuit is 50 KA /1s)but for building up a safety margin i can specify 65 KA/.5 or 85 KA/0.4 or 100 KA/0.4 . And i may give reasoning to the customer that higher the internal arc withstand of a panel more safer is the panel ( irrespective of the maximum prospective  short circuit current). Am i right here ?

 

However consultants are questioning on the building up of safety margin and ask under what circumstances can a current of 65 KA , 85 KA or 100 KA might flow in the system when maximum prospective short circuit current is 50 KA only ? 

 

 

 

 

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

PascalL
Lt. Commander PascalL Lt. Commander
Lt. Commander

Posted: ‎2020-10-27 08:41 AM

In response to rakeshNag123
1 Like
1
6729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-27 08:41 AM

Hi Rakesh,

 

Regarding your reply: "i may specify  is 50 KA /0.4 or 50 KA/0.3 (if prospective maximum short circuit is 50 KA /1s)but for building up a safety margin i can specify 65 KA/.5 or 85 KA/0.4 or 100 KA/0.4 . And i may give reasoning to the customer that higher the internal arc withstand of a panel more safer is the panel ( irrespective of the maximum prospective  short circuit current). Am i right here ?"

Yes you are right Rakesh.

 

About the second part of your reply: "under what circumstances can a current of 65 KA , 85 KA or 100 KA might flow in the system when maximum prospective short circuit current is 50 KA only ? "

If the Icc is 50KA you have no chance to have 65 or 85 or even 100KA.

If I make a parallels explanation...suppose you buy a car. The car is able to run at 190km/h. The speed is limited at 130km/h on the highway. So do you have any chance to exceed 130km/h? No but it is comfortable, the result is when you drive the noise will be lower, the reliability higher, the safety also.

To an assembly it is the same thing. Probably in case of internal arc the impact into the assembly will be less important, probably the MTTR(mind time to repair) will be better...we call that a safety margin.

Who can do more, can do less 🙂

Best regards,

PascalL.

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

rakeshNag123
Crewman rakeshNag123 Crewman
Crewman

Posted: ‎2020-10-27 11:36 AM

In response to PascalL
0 Likes
0
6725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-27 11:36 AM

Dear Pascal 

 

I am truly Delighted with the support extended and your  patient response to my queries . Will be glad if you can share any related literature for my reference and use ( if you already have any) 😊 and once again thank you ! 🙏 

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of