What is a circuit breaker and how does it work ?

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • What is a circuit breaker and how does it work ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-03-18 04:05 AM

4 Likes
7
4013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-18 04:05 AM

What is a circuit breaker and how does it work ?

Hi,

 

I'm kind of new in this activity, that's why I would like to understand what is a circuit breaker and how does it work ?

 

Thanks for your help!

Labels
  • Labels:
  • Connectivity
  • Power Availability
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-03-18 04:28 AM

3 Likes
3
4004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-18 04:28 AM

As per IEC standards 60947 the Circuit Breaker is defined as mechanical switching device, capable of making, carrying and breaking currents under normal circuit conditions and also making, carrying for a specified time and breaking currents under specified abnormal circuit conditions such as those of short circuit.

 

It has either Thermal magnetic release or Microprocessor based release system to take care of Protection functions.

 

Regards

Kiran Lagwankar

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-03-18 04:30 AM . Last Modified: ‎2021-03-18 04:35 AM

4 Likes
0
4003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-18 04:30 AM . Last Modified: ‎2021-03-18 04:35 AM

Hello M_Duca,

 

I'll try to get suitable information and explanations to you.
I got some very usefull web links and sites which give you a very wide and broad explanation.

As of now, I don't know your current electrical expertise.

So at first I would give you this website;

https://www.directenergyprotects.com/learning-center/electric/circuit-breaker-101#:~:text=How%20Do%2....

The site below also gives a good explanation (Base source of Schneider Electric itself);

https://www.wincogen.com/knowledge-base/how-do-circuit-breakers-work/

You can also watch a very informative inside look into a circuitbreaker when it trips in the following first part of an YT series;

https://www.youtube.com/watch?v=Cq55tbLtnlg

There is a whole range of different circuit breakers out there.
So if you need any more help or information, don't be shy to ask or contact.


Kind regards,

Rick

See Answer In Context

  • Tags:
  • Circuit Breakers
  • english
  • info
  • tutorial
  • what is
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-03-18 08:07 AM

4 Likes
0
3973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-18 08:07 AM

Hello,

for new comers in my team, I propose this one on YouTube. 

 

https://youtu.be/oYLIpN4RwEg 

 

Guys do you have another good one that you can share also ?

 

Thanks

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2021-03-18 04:21 AM . Last Modified: ‎2021-03-18 04:31 AM

2 Likes
0
4008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-18 04:21 AM . Last Modified: ‎2021-03-18 04:31 AM

Welcome among the community @Anonymous user. !!!

 

There is for sure someone here that can answer clearly your question.......

 

 

 

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-03-18 04:28 AM

3 Likes
3
4005
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-18 04:28 AM

As per IEC standards 60947 the Circuit Breaker is defined as mechanical switching device, capable of making, carrying and breaking currents under normal circuit conditions and also making, carrying for a specified time and breaking currents under specified abnormal circuit conditions such as those of short circuit.

 

It has either Thermal magnetic release or Microprocessor based release system to take care of Protection functions.

 

Regards

Kiran Lagwankar

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-03-18 04:30 AM . Last Modified: ‎2021-03-18 04:35 AM

4 Likes
0
4004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-18 04:30 AM . Last Modified: ‎2021-03-18 04:35 AM

Hello M_Duca,

 

I'll try to get suitable information and explanations to you.
I got some very usefull web links and sites which give you a very wide and broad explanation.

As of now, I don't know your current electrical expertise.

So at first I would give you this website;

https://www.directenergyprotects.com/learning-center/electric/circuit-breaker-101#:~:text=How%20Do%2....

The site below also gives a good explanation (Base source of Schneider Electric itself);

https://www.wincogen.com/knowledge-base/how-do-circuit-breakers-work/

You can also watch a very informative inside look into a circuitbreaker when it trips in the following first part of an YT series;

https://www.youtube.com/watch?v=Cq55tbLtnlg

There is a whole range of different circuit breakers out there.
So if you need any more help or information, don't be shy to ask or contact.


Kind regards,

Rick
  • Tags:
  • Circuit Breakers
  • english
  • info
  • tutorial
  • what is
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-03-18 08:07 AM

4 Likes
0
3974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-18 08:07 AM

Hello,

for new comers in my team, I propose this one on YouTube. 

 

https://youtu.be/oYLIpN4RwEg 

 

Guys do you have another good one that you can share also ?

 

Thanks

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-03-24 12:41 AM

In response to Anonymous user
2 Likes
2
3944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-24 12:41 AM

Thank you for your reply !

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2021-04-07 01:19 AM

In response to Anonymous user
1 Like
1
3831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-07 01:19 AM

Hello,

If you want to go more on detail, you can read Technical Folder made by our old Expert on the past

 

files (schneider-electric.com) 

 

I would advise you to read the ECT150 about MCCB and international standard IEC 60 947-2

Gregoire Brun
Breaker Product Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-04-20 05:33 AM . Last Modified: ‎2021-04-20 06:33 AM

In response to Gregoire_Brun
1 Like
0
3757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-20 05:33 AM . Last Modified: ‎2021-04-20 06:33 AM

Thank you for your answers !

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore