Thermal Sensors and monitoring solutions

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Thermal Sensors and monitoring solutions
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-03-23 05:56 AM

3 Likes
4
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-23 05:56 AM

Thermal Sensors and monitoring solutions

Dear community,

 

I am requested to upgrade electrical panels at customer's site.

They are requiring to have a thermal monitoring solution and condition based remote monitoring for their medium voltage secondary switchgears.

 

I've seen on this forum, but also elsewhere on the internet 🙂, that Schneider Electric thermal sensors easergy TH110 could be suitable for the job.

Where can I supply them? I cannot find them into the website.

Also, I'd like to have better understanding of the monitoring solutions related to the sensors.

 

Thanks for your help.

Labels
  • Labels:
  • Operations & Services
  • Power Availability
  • Products
  • Safety - Electrical Fire Prevention
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
L_Valentin
Lt. Commander L_Valentin
Lt. Commander

Posted: ‎2021-03-23 06:03 AM

1 Like
3
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-23 06:03 AM

Hello @Anonymous user 

 

Regarding the thermal sensors TH110 from Schneider, I think that there is no direct sales.

They are reserved for the EcoXperts partners of Schneider or directly built-in in new Medium Voltage switchgears.

 

Maybe someone from Schneider will confirm

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2021-03-23 06:13 AM . Last Modified: ‎2021-03-23 06:22 AM

In response to Anonymous user
0 Likes
1
2045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-23 06:13 AM . Last Modified: ‎2021-03-23 06:22 AM

Hello @Anonymous user 

 

Regarding your concerns about the condition monitoring solutions we can offer to you and your customer, I suggest you to check, among others, the following forum discussions:

 

  • "Connect Easergy Thermal Connect app with your Smart devices"
  • "Digital transformation of Power Systems is key for its durability and servicing costs"
  • "How modernize your electrical installation you can increase its durability and get smart insights for maintenance"

 

Also, check out the ones related to our EcoStruxure Asset Advisor software here:

  • "Want to know more about EcoStruxure Asset Advisor software?"
  • "EcoStruxure Asset Advisor….Live demo !!"

 

Hope this will help you as well....

 

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
L_Valentin
Lt. Commander L_Valentin
Lt. Commander

Posted: ‎2021-03-23 06:03 AM

1 Like
3
2053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-23 06:03 AM

Hello @Anonymous user 

 

Regarding the thermal sensors TH110 from Schneider, I think that there is no direct sales.

They are reserved for the EcoXperts partners of Schneider or directly built-in in new Medium Voltage switchgears.

 

Maybe someone from Schneider will confirm

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-03-23 06:06 AM

In response to L_Valentin
0 Likes
2
2049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-23 06:06 AM

Thank you @L_Valentin .

 

Very quick answer indeed !! 😁 👍

 

I'll contact Schneider customer care team then to find out how to move forward on this.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2021-03-23 06:13 AM . Last Modified: ‎2021-03-23 06:22 AM

In response to Anonymous user
0 Likes
1
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-23 06:13 AM . Last Modified: ‎2021-03-23 06:22 AM

Hello @Anonymous user 

 

Regarding your concerns about the condition monitoring solutions we can offer to you and your customer, I suggest you to check, among others, the following forum discussions:

 

  • "Connect Easergy Thermal Connect app with your Smart devices"
  • "Digital transformation of Power Systems is key for its durability and servicing costs"
  • "How modernize your electrical installation you can increase its durability and get smart insights for maintenance"

 

Also, check out the ones related to our EcoStruxure Asset Advisor software here:

  • "Want to know more about EcoStruxure Asset Advisor software?"
  • "EcoStruxure Asset Advisor….Live demo !!"

 

Hope this will help you as well....

 

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-03-23 06:17 AM

In response to J_Travostino
1 Like
0
2037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-23 06:17 AM

thanks @J_Travostino 

 

I'll check.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore