Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

The importance of "Ambient Temperature based Correction Factor," on the conductor sizing

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • The importance of "Ambient Temperature based Correction Factor," on the conductor sizing
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Power Distribution and Digital Support
Start a Topic
Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2020-11-22 11:53 PM . Last Modified: ‎2024-11-22 04:25 AM

0 Likes
0
3374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-22 11:53 PM . Last Modified: ‎2024-11-22 04:25 AM

The importance of "Ambient Temperature based Correction Factor," on the conductor sizing

Introduction : 

Wiring systems shall be selected and erected so as to be suitable for any temperature between the highest and the lowest local ambient temperature and to ensure that the limiting temperature in normal operation and the limiting temperature in case of a fault will not be exceeded. NOTE “Limiting temperature” means maximum continuous operating temperature.

Current Carrying Capacity:

The current to be carried by any conductor for sustained periods during normal operation shall be such that the temperature limit of the insulation is not exceeded. This requirement is fulfilled by application of Table 52.1, for the types of insulation given in this table.

Maximum operating temperatures for types of insulation:

The table 52.1 of the IEC standard is given here, and this explain the 'maximum operating temperature for different types of insulation.

Table 52-1.PNG

Correction Factor based on Temperature (Air):

For the Correction Factor based on Temperature; while the cable installation is present in AIR, the following table should be considered. This has a classification of correction factors based on the different insulations (PVC, XLPE) as well.

Kindly be noted that, the correction factor for the ambient air temperature of 30 *C can be considered as one (1).

B52_14.png

 

Correction Factor based on Temperature (Ground):

For the Correction Factor based on Temperature; While the cable installation is present in GROUND, the following table B.52.15 should be considered. This has a classification of correction factors based on the different insulations (PVC, XLPE) as well.

Kindly be noted that, the correction factor for the ambient air temperature of 20 *C can be considered as one (1).

B52_15.png

Labels
  • Labels:
  • Power Distribution Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore