Star Delta Motor Cable Calculation

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Star Delta Motor Cable Calculation
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Power Distribution and Digital Support
Eng_Omar
Crewman Eng_Omar
Crewman

Posted: ‎2021-10-25 06:32 AM . Last Modified: ‎2024-11-22 04:25 AM

0 Likes
3
6546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-25 06:32 AM . Last Modified: ‎2024-11-22 04:25 AM

Star Delta Motor Cable Calculation

Dear Experts,

 

I am used Ecodial 4.9.7 INT to calculate the requirements of the cable for the star delta 90KW motor and the distance for cable 20m, and i got the result as shown in the attached picture below.

my question is that result  ph : 1x70 mm CU represents the cables should i extend from main and delta contactors to the motor ? or i have to extend 1x35 mm Cu from the main and delta contactors to the motor ? .

 

Best Regards

Attachments
Labels
  • Labels:
  • Power Distribution Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Karthikeyan1
Lieutenant JG Karthikeyan1 Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-25 08:21 AM

0 Likes
2
6537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-25 08:21 AM

Hi Omar,

 

Thank you for the question.

 

As per your cable results in the attached screenshot, the calculated cable Cross-sectional area is Ph : 1X 70sq.mm and PE : 1X35sq.mm. This means, Ph- Phase conductor Cross-Sectional area is 1 run of 70 sq.mm cable and PE- Earthing conductor Cross-Sectional area is 1 run of 35sq.mm cable. 

So both the Phase and Earthing conductor of specified Cross-sectional area needs to be extended from main and delta contactor to the motor. 

 

Thanks & Regards,

Ecodial Expert Community

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Eng_Omar
Crewman Eng_Omar
Crewman

Posted: ‎2021-10-25 09:39 AM

In response to Karthikeyan1
0 Likes
1
6531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-25 09:39 AM

Hi Karthikeyan,

 

Thank you very much for your reply .

 

The thing that made me confusing that when i changed the motor control from star delta to direct the result of cable-stay same (please see attached picture ) .

 

As you know there are two cables in star delta that connect with both sides of the motor (the first cable comes from the main contactor and the second come from the delta contactor) , kindly can you explain to me how can i calculate the area of those cables by Ecodial ?

 

Best Regards

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Karthikeyan1
Lieutenant JG Karthikeyan1 Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-25 10:20 AM

In response to Eng_Omar
0 Likes
0
6528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-25 10:20 AM

Hi Omar,

 

 

Cable calculation on Ecodial is based on the full load current, voltage drop and certain other inputs. Not based on the starter type. If the full load current changes, then only the cable Cross-Sectional area will change. 

At present in Ecodial we cannot able size the different contactor cables on the Motor load. As a workaround, you can use the same Cross-sectional area of cable for both Main as well as the Delta contactor. 

 

Thanks & Regards,

Ecodial Expert Team

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of