Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-04 08:37 PM . Last Modified: 2024-11-22 04:25 AM
Hi
I have an example with an upstream breaker IC60 50A and dowstream IC60 10A.
Image shows selectivity up to 680A, curves do not overload as it is time current curves. Is there a curve in EcoDial where I can see the point where the two breakers overlap? only I can see now is 680A limit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-08 03:10 AM
Hello Larisa,
Thanks for reaching the EcoStruxure Power Design Forum.
Selectivity for the given MCBs
At the Ecodial application, the selectivity decision of the given MCBs is considered from the “selectivity tables” provided by the business.
The curve representation does not show the curve crossing (for the partial selectivity limit).
Yes, this part of the curve is not shown at the application.
Thanks & Regards,
Team - Ecodial Expert Support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-08 03:10 AM
Hello Larisa,
Thanks for reaching the EcoStruxure Power Design Forum.
Selectivity for the given MCBs
At the Ecodial application, the selectivity decision of the given MCBs is considered from the “selectivity tables” provided by the business.
The curve representation does not show the curve crossing (for the partial selectivity limit).
Yes, this part of the curve is not shown at the application.
Thanks & Regards,
Team - Ecodial Expert Support.