Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-04 08:37 PM . Last Modified: 2024-11-22 04:25 AM
Hi
I have an example with an upstream breaker IC60 50A and dowstream IC60 10A.
Image shows selectivity up to 680A, curves do not overload as it is time current curves. Is there a curve in EcoDial where I can see the point where the two breakers overlap? only I can see now is 680A limit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-08 03:10 AM
Hello Larisa,
Thanks for reaching the EcoStruxure Power Design Forum.
Selectivity for the given MCBs
At the Ecodial application, the selectivity decision of the given MCBs is considered from the “selectivity tables” provided by the business.
The curve representation does not show the curve crossing (for the partial selectivity limit).
Yes, this part of the curve is not shown at the application.
Thanks & Regards,
Team - Ecodial Expert Support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-08 03:10 AM
Hello Larisa,
Thanks for reaching the EcoStruxure Power Design Forum.
Selectivity for the given MCBs
At the Ecodial application, the selectivity decision of the given MCBs is considered from the “selectivity tables” provided by the business.
The curve representation does not show the curve crossing (for the partial selectivity limit).
Yes, this part of the curve is not shown at the application.
Thanks & Regards,
Team - Ecodial Expert Support.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.