Selectivity between MCCB / IC60
Hi
I have an example with an upstream breaker IC60 50A and dowstream IC60 10A.
Image shows selectivity up to 680A, curves do not overload as it is time current curves. Is there a curve in EcoDial where I can see the point where the two breakers overlap? only I can see now is 680A limit.
- Labels:
-
Power Distribution Software
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-08 03:10 AM
Hello Larisa,
Thanks for reaching the EcoStruxure Power Design Forum.
Selectivity for the given MCBs
At the Ecodial application, the selectivity decision of the given MCBs is considered from the “selectivity tables” provided by the business.
The curve representation does not show the curve crossing (for the partial selectivity limit).
Yes, this part of the curve is not shown at the application.
Thanks & Regards,
Team - Ecodial Expert Support.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-08 03:10 AM
Hello Larisa,
Thanks for reaching the EcoStruxure Power Design Forum.
Selectivity for the given MCBs
At the Ecodial application, the selectivity decision of the given MCBs is considered from the “selectivity tables” provided by the business.
The curve representation does not show the curve crossing (for the partial selectivity limit).
Yes, this part of the curve is not shown at the application.
Thanks & Regards,
Team - Ecodial Expert Support.