Selection of Short Circuit protection device (circuit breaker or fuse upstream of a SS or VFD) including type 1 and 2 coordination

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Selection of Short Circuit protection device (circuit breaker or fuse upstream of a SS or VFD) including type 1 and 2 coordin...
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
66
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
Anonymous user
Not applicable

Posted: ‎2020-11-05 11:01 AM

0 Likes
4
4926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-05 11:01 AM

Selection of Short Circuit protection device (circuit breaker or fuse upstream of a SS or VFD) including type 1 and 2 coordination

According to the FAQ

https://www.se.com/in/en/faqs/FA329751/

and relevant recommendations (Cahier technique no. 204) it would be helpful to get a “complete” guideline for selection of Short Circuit protection device (circuit breaker or fuse upstream of a SS or VFD) including type 1 and 2 coordination as well. Moreover it would be a good point if there is available the database of maximum permissible let-through energy of “well-known” Soft Starters and Variable Frequency Drivers models (e.g. Altistart 48).

 

 

  • Tags:
  • CB
  • Coordination
  • english
  • fuse
  • SoftStarter
  • vfd
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant

Posted: ‎2020-11-16 04:20 AM

2 Likes
1
4874
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-16 04:20 AM

Hello Fotini,

 

Your question is quite complex and I won't be able to give you a straightforward answer here.

 

We provide various tools and documentation to select overcurrent protection upstream Variable speed Drive and Soft-starter. Satrting with ATV and ATS catalog.

 

We also propose online configurator such as EcoStruxure Motor Control Configurator 

 

 

Soft starter are covered by IEC/EN 60947-4-2. This standard define test for type 1 and type 2 coordination. type 2 usualty requires ultra rapid fuses that are specified in ATS catalog. Coordination is usually difficult to check just by using energy withstand curves and let thhrough curve and often reuire test and/or simulation.

 

Variable speed drive are covered by IEC 61800-5-1 including internal short-circuit test. There is no concept of type 1 or type 2 coordination in that case. The withstand capacity with a specified overcurrent protection if necessary is given in VSD technical characteristics. When we provide "type 1" or "type 2" coordination table for VSD, the overcurrent protection is consistent with the VSD withstand, and the type 1 or type 2 performance refer to overcurrent protection and contactor. Again this can not be established without test or complex simulation.

 

Hope it helps,  Can you explain what is your design pain point behind ?

 

 

Regards

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2020-11-09 01:10 AM

0 Likes
0
4915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-09 01:10 AM

Hello Fotini,

This post has been moved to the Power Foundations forum.

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
Reply

Link copied. Please paste this link to share this article on your social media post.

MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant

Posted: ‎2020-11-16 04:20 AM

2 Likes
1
4875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-16 04:20 AM

Hello Fotini,

 

Your question is quite complex and I won't be able to give you a straightforward answer here.

 

We provide various tools and documentation to select overcurrent protection upstream Variable speed Drive and Soft-starter. Satrting with ATV and ATS catalog.

 

We also propose online configurator such as EcoStruxure Motor Control Configurator 

 

 

Soft starter are covered by IEC/EN 60947-4-2. This standard define test for type 1 and type 2 coordination. type 2 usualty requires ultra rapid fuses that are specified in ATS catalog. Coordination is usually difficult to check just by using energy withstand curves and let thhrough curve and often reuire test and/or simulation.

 

Variable speed drive are covered by IEC 61800-5-1 including internal short-circuit test. There is no concept of type 1 or type 2 coordination in that case. The withstand capacity with a specified overcurrent protection if necessary is given in VSD technical characteristics. When we provide "type 1" or "type 2" coordination table for VSD, the overcurrent protection is consistent with the VSD withstand, and the type 1 or type 2 performance refer to overcurrent protection and contactor. Again this can not be established without test or complex simulation.

 

Hope it helps,  Can you explain what is your design pain point behind ?

 

 

Regards

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-24 10:38 AM

0 Likes
0
4843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-24 10:38 AM

Hello Mathieu,

thank you for your reply. To be honest I was excepting that a test procedure is required to confirm the cooperation of the protection device and the motor starter but I am trying to find a more conservative way to define this cooperation in a general approach. To be more specific we are running a project and the client has already decided to work with ABB MCCB and gG fuses in the feeders but he likes more Schneider SS and VFDs. Now he is asking about coordination type 2 confirmation.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-26 02:12 AM

In response to MathieuGuillot
0 Likes
0
4828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-26 02:12 AM

Dear @MathieuGuillot,

it seems that @Anonymous user question (... a more conservative way to define this cooperation in a general approach) is similar to what I would like to ask.

Does Schneider carry out tests for each pair/combination of protection device/equipment (starter) to confirm coordination level or test procedure is done only for specific sizes of device/equipment followed by a calculation procedure which gives the result for the other pairs/combinations ? If so, could this calculation procedure be available for sharing ?

If this calculation procedure is not available could you send guidelines for a conservative selection ?

 

Thank you

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of