Power meters vs built-in metering in device

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Power meters vs built-in metering in device
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
Fabien_Mastrot
Lieutenant Fabien_Mastrot Lieutenant
Lieutenant

Posted: ‎2022-03-09 11:48 AM . Last Modified: ‎2022-03-16 01:34 AM

3 Likes
16
5036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-09 11:48 AM . Last Modified: ‎2022-03-16 01:34 AM

Power meters vs built-in metering in device

Hello,

what do think about the usage and application to have in Electrical Switchboard built-in metering in the circuit breaker or an external power meter . 

Do you have a vision of the type of application for both cases ?

Don t hesitate to share your point of view.

Thanks

 

Fabien Mastrot
EcoXpert global badge owner
Labels
  • Labels:
  • Connectivity
  • Energy management
  • Power Standards & Regulations
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BLeprettre
Crewman BLeprettre Crewman
Crewman

Posted: ‎2022-03-10 01:26 AM

In response to Anton_Balanescu
3 Likes
0
5002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-10 01:26 AM

Hello Anton and community,

 

Actually, several breakers offer measurement functions, like the CompactNSX and Masterpact ranges. The features and performance depend on the version of the Micrologic unit.The Masterpact MTZ even offers class-1 measurement performance per IEC 61557-12 and measures several electrical quantities.

 

Also FYI, the new version of the IEC 61557-12 standard - Equipment for testing, measuring or monitoring of protective measures - Part 12: Power metering and monitoring devices (PMD) introduces the notion of embedded Power Metering and monitoring Function (PMF) : a quality measurement function embedded into a device which main function is not to measure (e.g. a circuit breaker). Therefore, one could expect to see more and more good-quality embedded measurement capabilities in the future, when that makes sense.

 

Benoit

 

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2022-03-10 08:02 AM

In response to faisalamir
4 Likes
0
4969
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-10 08:02 AM

Hi,

 

It depends on your needs....

 

Micrologic X can propose Class1 Measurement according to IEC61557-12 and Event analysis related to open/close/trip events.

 

You will need an advanced Power Meter like PM8000 if you need to be conformant with some industry standards:

  • IEC 61000-4-30 for Power Quality Events analysis
  • IEEE 519 for Harmonics compliance,
  • EN 50160 for Voltage quality
  • IEC 62053-24 for Class 0.5S accuracy for reactive energy
  • Power Events waveform recording
  • COMTRADE Export
  • etc.

Regards,

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2022-03-11 06:50 AM

In response to T_Parks
2 Likes
0
4915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-11 06:50 AM

Hi,

 

We have used Powertag in the past on both Prisma switchboards, Compartmented switchboards and feeder pillars.

 

Prisma because of its open construction is great we got about three columns of out going devices monitored with 5% signal loss. Compartmented switchboards we get one column with modification to the internal steelwork and feeder pillars we have never had any problems.

 

We have linked them to Com'X via the concentrator and over an building internal network to other Com'X units without a problem. EMC appears to not be a problem.

 

Best reards,


Peter Hall.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 16
Anton_Balanescu
Ensign Anton_Balanescu
Ensign

Posted: ‎2022-03-09 11:57 PM

3 Likes
14
5012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-09 11:57 PM

Hello Fabien, Hello the Community

For sure I am convinced Power Metering should be embedded feature in breakerks.

 

However, as a large part of by business  stays at building electrical maintenance, I couldn't find better solution that upgrading old switchboards with Power Meters .

Considering that in 90% of cases, the need is to monitor energy consumptions, would there exist any breaker retrofit in this purpose?

 

Would somebody have found such (cost effective of course) solutions?

 

Looking forward to reading you!

Anton

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BLeprettre
Crewman BLeprettre Crewman
Crewman

Posted: ‎2022-03-10 01:26 AM

In response to Anton_Balanescu
3 Likes
0
5003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-10 01:26 AM

Hello Anton and community,

 

Actually, several breakers offer measurement functions, like the CompactNSX and Masterpact ranges. The features and performance depend on the version of the Micrologic unit.The Masterpact MTZ even offers class-1 measurement performance per IEC 61557-12 and measures several electrical quantities.

 

Also FYI, the new version of the IEC 61557-12 standard - Equipment for testing, measuring or monitoring of protective measures - Part 12: Power metering and monitoring devices (PMD) introduces the notion of embedded Power Metering and monitoring Function (PMF) : a quality measurement function embedded into a device which main function is not to measure (e.g. a circuit breaker). Therefore, one could expect to see more and more good-quality embedded measurement capabilities in the future, when that makes sense.

 

Benoit

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

faisalamir
Lieutenant faisalamir Lieutenant
Lieutenant

Posted: ‎2022-03-10 04:49 AM

In response to Anton_Balanescu
3 Likes
4
4980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-10 04:49 AM

Hi Anton,

 

Maybe you want to look at our Schneider solution for wireless energy sensor 

 

This solution can be applied with the existing MCB and MCCB 

 

Hope it helps  

 

Regards,

Faisal 

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2022-03-10 08:02 AM

In response to faisalamir
4 Likes
0
4970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-10 08:02 AM

Hi,

 

It depends on your needs....

 

Micrologic X can propose Class1 Measurement according to IEC61557-12 and Event analysis related to open/close/trip events.

 

You will need an advanced Power Meter like PM8000 if you need to be conformant with some industry standards:

  • IEC 61000-4-30 for Power Quality Events analysis
  • IEEE 519 for Harmonics compliance,
  • EN 50160 for Voltage quality
  • IEC 62053-24 for Class 0.5S accuracy for reactive energy
  • Power Events waveform recording
  • COMTRADE Export
  • etc.

Regards,

Romain POLETTE
Solution Architect - France Operations
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Fabien_Mastrot
Lieutenant Fabien_Mastrot Lieutenant
Lieutenant

Posted: ‎2022-03-10 09:41 PM

In response to Anton_Balanescu
1 Like
7
4939
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-10 09:41 PM

Hello Anton,

Thanks for your application case , your proposal is really relevant. Any other application recommandation ?

In case of issue of space in a panel a solution with class 2 metering can be also proposed by changing the trip unit of the MCCB. 

Looking forwaed to ready you guys on other application. 

Fabien

Fabien Mastrot
EcoXpert global badge owner
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

T_Parks
Lieutenant T_Parks
Lieutenant

Posted: ‎2022-03-11 06:38 AM

In response to faisalamir
0 Likes
1
4917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-11 06:38 AM

Hello @faisalamir,

 

Can you tell me more about your powertag sensors?

Is there technical limitations in term of quantity in a switchboard?

What about EMC?

 

And also, is it possible to link it to a Schneider electric Com'X (I didn't find it into your document)?

or is it compatible with any other manufacturer gateways/concentrators?

 

Thanks for information.

 

@community members,

I'd like to hear your experiences with this product as well......

 

 

T_Parks
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2022-03-11 06:50 AM

In response to T_Parks
2 Likes
0
4916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-11 06:50 AM

Hi,

 

We have used Powertag in the past on both Prisma switchboards, Compartmented switchboards and feeder pillars.

 

Prisma because of its open construction is great we got about three columns of out going devices monitored with 5% signal loss. Compartmented switchboards we get one column with modification to the internal steelwork and feeder pillars we have never had any problems.

 

We have linked them to Com'X via the concentrator and over an building internal network to other Com'X units without a problem. EMC appears to not be a problem.

 

Best reards,


Peter Hall.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anton_Balanescu
Ensign Anton_Balanescu
Ensign

Posted: ‎2022-03-11 10:16 AM

In response to Fabien_Mastrot
1 Like
6
4903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-11 10:16 AM

Hi Fabien , 

 

Regarding other applications I can testify, I would raise one I get more and more required, in Office buildings: property managers and landlords specify MID certified meters, to comply with regulations to enable power sub-billing .

 

Would that orient this discussion into MID-compliance specific approaches?

 

Best regards

Anton

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-03-29 07:41 AM

In response to Anton_Balanescu
0 Likes
5
4610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-29 07:41 AM

Did some of you use the CT bloc we propose with ComPacT NSX offer ?

 

 

 

Gregoire Brun
Breaker Product Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2022-03-30 01:07 AM

In response to Gregoire_Brun
1 Like
4
4566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-30 01:07 AM

Can anyone afford to use the CT blocks offered?

I know that they are convenient but their pricing is way too optimistic. Have a look at what it costs to install 3 x CT's (worst case) and wire up. The price of the CT blocks are probably 300-400% of CT's.

Please remember new technology is all well and good but you still need to compete in the market and be aware of what other manufacturers are offering.

Some companies would like to offer nothing but SE products, however cost considerations need to be taken into account. It is a competitive market out there after all.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2022-03-30 01:41 AM

In response to Peter_Hall
1 Like
1
4563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-30 01:41 AM

Agreed in full with @Peter_Hall 

Especially here on the Dutch Market.

The Dutch are famous for; kijken, kijken niet kopen.
Roughly translated to; look, look, not buying.

We see alot of cool features and technologies but as soon as they ask or we mention

the price tag its considered expensive or not cost-efficient / an necessity.

It completely depends on the project and client as well ofcourse.

 


Kind regards,

Rick
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2022-03-30 01:51 AM

In response to RHH
0 Likes
0
4554
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-30 01:51 AM

Glad to here that you agree.

It is by no means any criticism of the current offers. 

Just like any company we all have to have ideas that we would like to implement. However, if the costs are just too prohibitive to offer, then we all need to look elsewhere for alternative offers/manufacturers.

Is it not better to sell many units at a price that makes sense to all parties rather than not sell units and have stock sat on the shelf which eventually you have to offer additional discount to sell? 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anton_Balanescu
Ensign Anton_Balanescu
Ensign

Posted: ‎2022-03-30 01:57 AM . Last Modified: ‎2022-03-30 05:08 AM

In response to faisalamir
0 Likes
0
4548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-30 01:57 AM . Last Modified: ‎2022-03-30 05:08 AM

Warm thanks, @faisalamir, your document is really amazingly comprehensive through technologies & power ranges!

 

This I will for sure use to evaluate built-in metering solutions in next projects;

 

best regards.

Anton

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-03-30 08:07 AM

In response to Peter_Hall
0 Likes
1
4518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-30 08:07 AM

Hi Peter, I know that price product could be suprising some time, 

But  time to install and fixe 3 CT compare to the CT's bloc who is directly fixed to the breaker, and space improvment ,

I 've imagine it could be an advantage...

And  between Powertag to a CT block, what is for you advantage between this 2 solutions ?

 

Gregoire Brun
Breaker Product Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sesa97267_bridg
Lieutenant JG sesa97267_bridg Lieutenant JG
Lieutenant JG

Posted: ‎2022-03-30 09:27 AM

0 Likes
0
4512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-30 09:27 AM

Hi Fabien,

 

from a techno-trend perspective, the approach for distributed systems where sensing, actuating and computation are separated would rather invite us not to embed sensing in the CB.

A single sensor shall in the future be able to feed simultaneously several computation units. Dedicated computation units could have dedicated features (CB Protection, Power Quality analysis..) or these computations could be performed in a single unit.

 

Not for tomorrow, just for the day after 😉

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2022-03-30 09:35 AM

In response to Gregoire_Brun
1 Like
0
4510
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-30 09:35 AM

Hi Gregoire,

Thanks for your reply.

I get your theory. However, in a Prisma switchboard (our standard offer) the space saving is not great compared to CT's.

The problem relating to cost is even great using PowerTag. Again a great product which we have used, but costs again are an even greater issue with this offer.

 

Best regards,

 

Peter Hall.   

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of