Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-30 01:29 AM
Hello @geir_eas_no_bfo ,
Goal of the Panel Server is to replace all previous following gateways:
Hardware of the Panel Server does not allow to integrate a dedicated port to stack IFMs through TRV00217.
This was not possible by design. Do not forget that Panel Server integrates a specific chip dedicated to Cybersecurity. This take more place on PCBA for a footprint identical to the IFE. IFE is cybersecured through its FW updates.
To connect IFM to Panel Server, we recommend the same adapter as the Link150 / IFM.
IFE is still commercialized and maintained because this is the gateway dedicated to breaker ULP system. IFE is both ULP to Modbus TCP and Modbus Serial to Modbus TCP gateway. IFE allows you to optimize breaker system design:
IFE is not compatible with Energy Hub.
Knowing that, you can choose the better gateway for your needs.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-30 01:29 AM
Hello @geir_eas_no_bfo ,
Goal of the Panel Server is to replace all previous following gateways:
Hardware of the Panel Server does not allow to integrate a dedicated port to stack IFMs through TRV00217.
This was not possible by design. Do not forget that Panel Server integrates a specific chip dedicated to Cybersecurity. This take more place on PCBA for a footprint identical to the IFE. IFE is cybersecured through its FW updates.
To connect IFM to Panel Server, we recommend the same adapter as the Link150 / IFM.
IFE is still commercialized and maintained because this is the gateway dedicated to breaker ULP system. IFE is both ULP to Modbus TCP and Modbus Serial to Modbus TCP gateway. IFE allows you to optimize breaker system design:
IFE is not compatible with Energy Hub.
Knowing that, you can choose the better gateway for your needs.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-30 02:21 AM
Hi Romain,
Thanks for the detailed good answer as always:)
Still think that modbus slave port could be more efficent on the PAS, with RJ45 connector and some emty space/slot so PAS could stand next to IFM without a gap.
PAS is unfortunately still no 1 to 1 replacment for ComX, as it can not send CSV over e-mail.
(Creates many replacement issues, where ComX sends csv-data to third party systems)
BR
GIA