Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-03 10:43 AM . Last Modified: 2022-06-16 10:43 PM
There is the following query, in the Micrologic Model NSX 400N device. The energy consumption parameter (kW h) is not displayed.
What is needed to obtain this parameter?
Attached sensors captured in DCE.
Regards
Caroll
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-06 10:55 PM
Dear Caroll,
Energy is available on the Modbus communication interface in the Standard dataset at the following address:
Type of data is INT64.
Please, read carefully below how to calculate Energy:
See guide link below for details.
ComPact NS XModbus Communication Guide User guide | Schneider Electric
Best regards
Ludovic
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-06 01:20 PM
Dear Ludovico
It is the Micrologic 5.3 E.
It is required to read the energy in communication.
Currently the parameter is displayed from the same micrologic.
Attached image
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-06 10:55 PM
Dear Caroll,
Energy is available on the Modbus communication interface in the Standard dataset at the following address:
Type of data is INT64.
Please, read carefully below how to calculate Energy:
See guide link below for details.
ComPact NS XModbus Communication Guide User guide | Schneider Electric
Best regards
Ludovic