MX shunt trip release coil 220 - 240 V, Is the constant voltage supply to the coil is harmful to it?
  • Power Distribution IEC
  • MX shunt trip release coil 220 - 240 V, Is the constant voltage supply to the coil is harmful to it?
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
PK_1988
PK_1988
Cadet
Posted: ‎2025-09-02 07:25 AM
355
Hello, Everyone!
I couldn't find the information about whether the constant voltage supply to the coil of MX shunt trip release will be harmful to the coil or not. We use 2 MX shun trip releases to shut down the breakers in the event of the fire alarm system activation, so that means the voltage will be constantly present on the MX coils while commissioning the FAS system.
Thanks in advance.
  • Knowledge
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander
Posted: ‎2025-09-03 02:05 AM
Hello @PK_1988, thank you for your post, we'll come back to you!
NeiB
Lt. Commander NeiB Lt. Commander
Lt. Commander
Posted: ‎2025-09-12 09:45 AM . Last Modified: ‎2025-09-12 10:17 AM
Hi @PK_1988 ,
Hope you are well.
The MX shunt coil for circuit breakers normally works under voltage, that is, while there is voltage the circuit breaker is open, if there is no voltage the circuit breaker is closed closed.
Tell us which is the model of your circuit breaker so we can check for the MX Shunt information.
Best Regards,
Neide