Lightning surge protection: Two is better than one!

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Lightning surge protection: Two is better than one!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Related Products
product field
Schneider Electric
Surge Protection Devices

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Power Distribution and Digital Support
Start a Topic
Anonymous user
Not applicable

Posted: ‎2021-03-16 07:20 AM . Last Modified: ‎2022-01-25 11:22 PM

1 Like
2
1753
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-16 07:20 AM . Last Modified: ‎2022-01-25 11:22 PM

Lightning surge protection: Two is better than one!

What everybody knows...


To protect low voltage installations against power surges caused by lightning, surge protection devices (SPDs) should be installed as far upstream as possible. Why? To drive the awesome power from lightning strikes to the ground and stop it from spreading down through the installation.

What everybody doesn’t know...


Such protection may not be enough to protect sensitive electrical and electronic equipment – especially if it’s some distance away from the primary upstream surge protector.

 

How do long cables affect voltage in equipment?

If the length of the cable between the primary surge arrester (in the incoming switchboard) and the equipment you want to protect is too long, oscillations and wave reflections may lead to sharp voltage rises in the equipment. In fact, such rises may exceed the arrester’s voltage protection level (Up) and rise to levels that are twice as high as Up.

The figure below shows how the maximum voltage curve at the end of a cable is determined by cable length for an incident wave-front voltage of 4kV/µs:

 

image 1.png

 

Why does voltage double?

 

Lightning emits electromagnetic waves in frequencies measured in hundreds of kHz and MHz. The voltage variations are so fast there is no way you can assume voltage is the same at any point in the cable. And the incident surge front may further excite oscillations caused by the cable’s own resonant frequencies (e.g. parasitic capacitances or filtering).

What is taking place is known as total internal reflection. This is when a wave travelling through a medium hits the medium’s boundary at an angle that is greater than its particular critical angle.

A useful way to picture total internal reflection is a wave that crashes against a wall. The wave represents the voltage wave and its height the wave’s magnitude. When it crashes against the wall, it doubles in height and flows back whence it came.

 

image 2.png

 

What is the best solution for failsafe lightning protection?

 

When reflection occurs over cable lengths shorter than 10 metres, voltage surge fronts in buildings may be disregarded. But at anything over 30 metres there is a serious risk that the voltage wave magnitude will double.

The solution is to add a second surge protector (or arrester) as close as possible to the equipment you want to protect. The second device doesn’t need to have as high a discharge capacity as the primary arrester; Imax <8kA (8 / 20) is enough. That’s because the primary surge protection device has already diverted the lightning current to ground.

 

image 3.png

 

Find out more about surge protection and how we can support your installations here.

 

Labels
  • Labels:
  • Safety - Electrical Fire Prevention
  • Safety - People Safety
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Gingko_Elec
Lieutenant JG Gingko_Elec
Lieutenant JG

Posted: ‎2021-03-19 08:34 AM

0 Likes
0
1732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-19 08:34 AM

I find a lot of residential customers won't pay out for surge protection because they don't see the benefit. How do you convince them?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-03-24 09:48 AM

1 Like
0
1723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-24 09:48 AM

Hi @Gingko_Elec 

We fully understand that some customers may need convincing of the benefits of SPDs, so we created a guide to help explain what surge protection is and why it's a worthwhile investment. You can share that guide with your customers to demonstrate the advantages of having surge protection.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore