Is a rated 240V RCBO be safe when applied in a 110V system ?

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Is a rated 240V RCBO be safe when applied in a 110V system ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
psiiot2021
psiiot2021
Cadet

Posted: ‎2022-12-27 06:29 PM

0 Likes
9
3240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-27 06:29 PM

Is a rated 240V RCBO be safe when applied in a 110V system ?

Recently, I have a rated 240V RCBO (model no. iC60N C6 30mA 240V) applied in a 110V system. when I press the test button, it won't trip. So Is it still safe to use in this scenario?

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2023-01-04 12:32 AM . Last Modified: ‎2023-01-04 12:35 AM

2 Likes
1
3197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-04 12:32 AM . Last Modified: ‎2023-01-04 12:35 AM

hello @psiiot2021 

This product is not adapted for 110V application, that's why trip button doesn't work. we recommend to change your product with an adapted product for 110V network.

Check if A9V01225 Vigi iC60 2P 25A 30mA AC is available in your country, if not, please contact customer care center in your country to find the best solution for your application.

Gregoire Brun
Breaker Product Expert

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2023-01-04 12:32 AM . Last Modified: ‎2023-01-04 12:35 AM

2 Likes
1
3198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-04 12:32 AM . Last Modified: ‎2023-01-04 12:35 AM

hello @psiiot2021 

This product is not adapted for 110V application, that's why trip button doesn't work. we recommend to change your product with an adapted product for 110V network.

Check if A9V01225 Vigi iC60 2P 25A 30mA AC is available in your country, if not, please contact customer care center in your country to find the best solution for your application.

Gregoire Brun
Breaker Product Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

AABBCC
Crewman AABBCC
Crewman

Posted: ‎2024-09-05 08:59 AM

In response to Gregoire_Brun
0 Likes
0
2413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-05 08:59 AM

Hi Mr.Brun

i am surging 1P+N C16A 30ma Type A RCBO

it has to work on 220/127VAC 1F+N =127V

                                                   F+F = 220VAC

have schneider Electric this product 

i am in the Caribbean

 

awaiting for your soonest reply

regards

 

Arthur 

mail -aboye@hitess.com

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2024-09-06 01:37 AM

0 Likes
5
2395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-06 01:37 AM

hello @AABBCC 

On witch country you are exactly please, to help you review local catalogue of what can be avalable on your country.

Gregoire Brun
Breaker Product Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

AABBCC
Crewman AABBCC
Crewman

Posted: ‎2024-09-06 06:23 AM

In response to Gregoire_Brun
0 Likes
2
2380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-06 06:23 AM

hi Brun

tks for your reply

We are on the ABC island and Surinam

and we have 220/120Vac 

and need thus RCBO 

 

i hope you can help me

regards

 

Reply

Link copied. Please paste this link to share this article on your social media post.

AABBCC
Crewman AABBCC
Crewman

Posted: ‎2024-09-07 07:23 AM

In response to AABBCC
0 Likes
1
2349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-07 07:23 AM

hi Mr Brun

reminder

Reply

Link copied. Please paste this link to share this article on your social media post.

AABBCC
Crewman AABBCC
Crewman

Posted: ‎2024-09-07 07:28 AM

In response to AABBCC
0 Likes
0
2345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-07 07:28 AM

HI MR BRUN 

FORGOT TO ADD THIS IT HAS TO BE A RCBO CLASS TYPE A OR A-SI

 

REGARDS

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

AABBCC
Crewman AABBCC
Crewman

Posted: ‎2024-09-10 04:10 PM

In response to Gregoire_Brun
0 Likes
1
2281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-10 04:10 PM

hi Brun

tks for your reply

We are on the ABC island and Surinam

and we have 220/120Vac 

and need thus RCBO 

 

i hope you can help me

regards

Reply

Link copied. Please paste this link to share this article on your social media post.

AABBCC
Crewman AABBCC
Crewman

Posted: ‎2024-09-13 04:47 AM

In response to AABBCC
0 Likes
0
2248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-13 04:47 AM

hi Brun

tks for your reply

We are on the ABC island and Surinam

and we have 220/120Vac 

and need thus RCBO 

 

i hope you can help me

regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2024-09-30 01:52 AM

0 Likes
0
2141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-30 01:52 AM

hello @AABBCC 

Sorry, I was under vacation. 

Could you purchase it to French Guiana? in this case I can advise you some reference issue from french catalogue.

 

 

Gregoire Brun
Breaker Product Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore