ISFL fuseways

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • ISFL fuseways
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2021-04-02 01:03 AM

1 Like
6
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-02 01:03 AM

ISFL fuseways

Good morning,

Can some from Schneider contact me regarding ISFL fuseways? 
i’m looking at feeder pillar applications, these fuse ways are not too common at present in the UK.

Labels
  • Labels:
  • Power Availability
  • Products
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2021-04-06 09:00 AM

In response to Peter_Hall
1 Like
0
1906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-06 09:00 AM

Hello @Peter_Hall 

 

Regarding your question about the CT's voltage supply:

The FuPacT internal CTs do not request any voltage supply (self-powered)

As a result, there is no internal connection for voltage supply pickup so if you want to meter the energy, you will have to take it from the busbars.

 

Regarding the metering device, you are totally right: it is better to use the “empty plastic box” as shown in page B-34 (see pict below)

Catalog Capture B-34.JPG

However, for an ISFL160, the dimensions are 46x46.

Unfortunately, a PowerLogic PM8000 is 96x96.

So it cannot be adapted on a FuPacT ISFL160.

 

As a result, I suggest you to use an ISFL250 (with its "empty plastic box") that would be able to welcome a PM8000 (96x96).

Metering on FuPacT ISFL250.JPG

 

 

Also, let me share with you the link toward the FuPacT 2020 catalog here

(We then could be aligned on the pages 😉)

 

Hope this answers your questions. 

Do note hesitate to come back to us....

 

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2021-04-02 02:33 AM

0 Likes
5
1956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-02 02:33 AM

Hello @Peter_Hall ,

 

What kind of information do you need regarding ISFL fuses? 

 

 

Thanks.

 

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2021-04-02 04:02 AM

In response to J_Travostino
0 Likes
4
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-02 04:02 AM

Hi Julien,

Thank for coming back to me.

We are especially interested in how to fit metering to the fuse ways. It would appear that we can fit CT's (or a single CT) into the 'body' of the fuse way to achieve a neat solution. We can then meter via a DIN96 device in a housing on the fuse way. Our customer is looking at one of your PM8000 series meters. Will these fit?

 

Best regards,

 

Peter Hall. 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2021-04-02 05:33 AM

In response to Peter_Hall
0 Likes
3
1948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-02 05:33 AM

Thanks for clarification @Peter_Hall 

 

It is clearer now. 

we will be back to you soon. 

let s keep in touch. 

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jean_Commeignes
Administrator Jean_Commeignes Administrator
Administrator

Posted: ‎2021-04-06 02:29 AM

In response to J_Travostino
0 Likes
2
1920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-06 02:29 AM

Hello Peter,

 

Your question is quite interesting one...

To get a chance to answer it, we need to feed as accurately as possible (and I know you are looking yourself for additional clues)  whatever  about mechanical integration of Fuse with CT's.

For time being, looking at ISFL160 instruction sheet, we can't understand how  integrating CT.

=> could you tell us please which CT and how you would mount it within ISFL160?

 

Then, though it is not as important topic as above one, would be useful to know if you would go for :

  • embedded display PM8000 
  • or would a remote display version OK?

Best

Jean COMMEIGNES
Schneider Electric Community Manager for Power & Building
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2021-04-06 04:24 AM

In response to Jean_Commeignes
0 Likes
1
1917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-06 04:24 AM

Good afternoon Jean,

 

Thank you for responding to me.

 

Looking at your FuPact catalogue there appears to be 2 solutions for CT's to fitted to the ISFL160 fuse way. Either:

 

1. Single pole 150/5A Class 1.

2. Three pole 150/5A Class 1.

 

The above are shown on page A-52.

 

How do we pickup a Voltage supply from the fuse way? Is this via the main busbars? or is there an internal connection?

 

In regard to metering. It would be preferable to mount the power meter within the 'plastic box' as mentioned in Page A-60 of the catalogue. Is this possible with the PM8000? (our customers specified meter).

 

Best regards,

 

Peter Hall.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2021-04-06 09:00 AM

In response to Peter_Hall
1 Like
0
1907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-06 09:00 AM

Hello @Peter_Hall 

 

Regarding your question about the CT's voltage supply:

The FuPacT internal CTs do not request any voltage supply (self-powered)

As a result, there is no internal connection for voltage supply pickup so if you want to meter the energy, you will have to take it from the busbars.

 

Regarding the metering device, you are totally right: it is better to use the “empty plastic box” as shown in page B-34 (see pict below)

Catalog Capture B-34.JPG

However, for an ISFL160, the dimensions are 46x46.

Unfortunately, a PowerLogic PM8000 is 96x96.

So it cannot be adapted on a FuPacT ISFL160.

 

As a result, I suggest you to use an ISFL250 (with its "empty plastic box") that would be able to welcome a PM8000 (96x96).

Metering on FuPacT ISFL250.JPG

 

 

Also, let me share with you the link toward the FuPacT 2020 catalog here

(We then could be aligned on the pages 😉)

 

Hope this answers your questions. 

Do note hesitate to come back to us....

 

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore