New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
IEC 61439-1 & 2 Ed 3 Changes Detailed
Power Distribution and Digital Support
Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-04-2012:22 AM. Last Modified: 2022-01-2612:17 AM
IEC 61439-1 & 2 Ed 3 Changes Detailed
IEC Top Image.JPG
After nine years of committee debate the 3rd Editions of IEC 61439-1 and IEC 61439-2, the standards for power switchgear and controlgear assemblies, have been published.
The new editions include changes, the significance of which will affect the way assemblies are specified and used. All the changes are either a recognition of the changing needs of assemblies in the market, technical advances, further options in design verification or clarifications.
These changes have been made with simple objectives in mind; ensuring assemblies are fit for purpose and there is a clear understanding of the capabilities of the assembly between specifier and manufacturer.