Explain who can issue certificate and is there a way to check criteria for certificate as per IEC

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Explain who can issue certificate and is there a way to check criteria for certificate as per IEC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-07-04 05:28 AM . Last Modified: ‎2021-10-27 11:03 AM

0 Likes
2
3333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:28 AM . Last Modified: ‎2021-10-27 11:03 AM

Explain who can issue certificate and is there a way to check criteria for certificate as per IEC

As a specifier i face the challenge when one company say they comply to IEC61439 and other say they have test report/s as per IEC61439

Labels
  • Labels:
  • Power Standards & Regulations
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MaheshReganti
Ensign MaheshReganti Ensign
Ensign

Posted: ‎2020-07-11 05:29 PM . Last Modified: ‎2020-07-11 05:42 PM

0 Likes
0
3316
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-11 05:29 PM . Last Modified: ‎2020-07-11 05:42 PM

This is a common challenge every end customer / consultants are facing to differentiate between test reports and certificate.

IEC clearly defines under two standards this criteria . IEC 17065 & IEC 17025

 

IEC 17065 : Confirmity Assessment Body Accreditation - Confirmity assessment Bobies certifies products, processes and services .An organization which complies to this standard are approved to issues IEC certificates. This is based on the organization capability to perform all the three design verification defined in IEC 61439-1 ie Testing, Comparison and Assessment.

 

IEC 17025 : Test Laboratory Acceditation - General requirement for testing and caliberating laboratories. This is based on the organization capability to do only one of the three design verifications defined in IEC 61439-1 ie Testing. These organizations are not assessed and confirmed to execute Comparison and Assessment. An organization which complies to only test criteria are approved to issues IEC test reports and not certificates.

 

Attached webinar by lab expert to one of the esteemed customer is elaborating the above topics and more. Though the presentation is bit long, initial 20 minutes of the webinar will clarify the above questions.

https://vimeo.com/427347241/c75cf0cef5

 

Hope this clarifies your concern 

 

 

Mahesh Reganti
Product manager - Blokset, LV switchboard

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

PascalL
PascalL Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2020-09-15 01:00 AM

1 Like
0
3169
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-15 01:00 AM

To comply and get a certification according to IEC61439-1/2 it is not a menu "a la carte". It is not allowed to choice the test that you are ready to perform. You need to perform ALL the tests required by the standard. it was the concept of the IEC60439 authorizing to be partially type tested. This concept was killed with the IEC61439. If competitors try to speak and present tests reports according to IEC61439 against a certificate IEC61439 you are not comparing apple to apple. You can be sure they are trying to avoid some difficult performances hiding some of them. You have to be proud of your certificate and don't hesitate to explain the much more value compared with tests report.

Pascal Lepretre, Edison expert.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
MaheshReganti
Ensign MaheshReganti Ensign
Ensign

Posted: ‎2020-07-11 05:29 PM . Last Modified: ‎2020-07-11 05:42 PM

0 Likes
0
3317
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-11 05:29 PM . Last Modified: ‎2020-07-11 05:42 PM

This is a common challenge every end customer / consultants are facing to differentiate between test reports and certificate.

IEC clearly defines under two standards this criteria . IEC 17065 & IEC 17025

 

IEC 17065 : Confirmity Assessment Body Accreditation - Confirmity assessment Bobies certifies products, processes and services .An organization which complies to this standard are approved to issues IEC certificates. This is based on the organization capability to perform all the three design verification defined in IEC 61439-1 ie Testing, Comparison and Assessment.

 

IEC 17025 : Test Laboratory Acceditation - General requirement for testing and caliberating laboratories. This is based on the organization capability to do only one of the three design verifications defined in IEC 61439-1 ie Testing. These organizations are not assessed and confirmed to execute Comparison and Assessment. An organization which complies to only test criteria are approved to issues IEC test reports and not certificates.

 

Attached webinar by lab expert to one of the esteemed customer is elaborating the above topics and more. Though the presentation is bit long, initial 20 minutes of the webinar will clarify the above questions.

https://vimeo.com/427347241/c75cf0cef5

 

Hope this clarifies your concern 

 

 

Mahesh Reganti
Product manager - Blokset, LV switchboard
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

PascalL
PascalL Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2020-09-15 01:00 AM

1 Like
0
3170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-15 01:00 AM

To comply and get a certification according to IEC61439-1/2 it is not a menu "a la carte". It is not allowed to choice the test that you are ready to perform. You need to perform ALL the tests required by the standard. it was the concept of the IEC60439 authorizing to be partially type tested. This concept was killed with the IEC61439. If competitors try to speak and present tests reports according to IEC61439 against a certificate IEC61439 you are not comparing apple to apple. You can be sure they are trying to avoid some difficult performances hiding some of them. You have to be proud of your certificate and don't hesitate to explain the much more value compared with tests report.

Pascal Lepretre, Edison expert.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore