[Electrical Fire Prevention 28 January 2020 webinar] - Why do we need TH110 and HeatTag in same time?

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • [Electrical Fire Prevention 28 January 2020 webinar] - Why do we need TH110 and HeatTag in same time?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Jean_Commeignes
Administrator Jean_Commeignes Administrator
Administrator

Posted: ‎2020-01-28 12:53 AM

1 Like
4
3056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-28 12:53 AM

[Electrical Fire Prevention 28 January 2020 webinar] - Why do we need TH110 and HeatTag in same time?

This question has been raised during January 28th 2020 webinar: 

 

Why do we need TH110 and HeatTag in same time?

 

Let us see Expert answer.

 

 

Best regards

Jean Commeignes

Power & Building Exchange Community Manager 

Jean COMMEIGNES
Schneider Electric Community Manager for Power & Building
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-01-30 09:16 AM

2 Likes
1
3044
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-30 09:16 AM

TH110 gives advance signal on the rise in temperature which would be as a result of overload/loose termination/inadequate tightness in bus bars/lesser contact pressure in floating contacts of breakers. Alerts prevents major accident, loss of life and distruption in power .Keeps O&M team free from continous monitoring and free up their energy&time , Helps to monitor critical areas which are non accessible in normal time.  I am not clear about What's heat tag?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2020-01-30 09:16 AM

2 Likes
1
3045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-30 09:16 AM

TH110 gives advance signal on the rise in temperature which would be as a result of overload/loose termination/inadequate tightness in bus bars/lesser contact pressure in floating contacts of breakers. Alerts prevents major accident, loss of life and distruption in power .Keeps O&M team free from continous monitoring and free up their energy&time , Helps to monitor critical areas which are non accessible in normal time.  I am not clear about What's heat tag?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-01-30 09:42 AM

In response to Anonymous user
1 Like
0
3042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-30 09:42 AM

Hi All

 

Got to know on Heat Tag from one of the Schneider article on Electrical fire prevention guide and  is as below:

 

Schneider Electric’s Solution: HeatTag
HeatTag is neither a fire detector nor a smoke detector. As
shown in Figure 1.9, between 170°C and 200°C, typical
LV cable-insulation materials, such as PVC / XLPE / EPR,
are subject to invisible transformation. These abnormal
conditions can be detected by HeatTag.

HeatTag detects and analyzes the different gases and particles
in the air of the switchboard (14 gases measured, along with
particles), applies a complex algorithm to select internal cable
issues from other phenomena, and can distinguish abnormal
situations that indicate a cable is overheating and sends an
alarm via email or SMS.

Reply

Link copied. Please paste this link to share this article on your social media post.

TewfikBoudiba
Commander TewfikBoudiba Commander
Commander

Posted: ‎2020-01-30 10:29 AM

0 Likes
0
3037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-30 10:29 AM

A fire in an electrical cabinet can come from overheating or deterioration of the connections and also from excessive heating of the cables.
The TH110 allows continuous monitoring of the temperature at the level of connections through which a minimum current of 5A is passed. The TH110 cannot monitor the condition of the cables over their entire length, Schneider Electric has thought of adding an advanced gas analyzer by air suction. The analysis of the air will make it possible to detect the odorless particles which emanate from the cable sheaths and which are predictors of a high probability of a fire starting.
By combining both the thermal monitoring of connections and cables, we ensure better prevention of the risk of electrical fire.


Kind Regards,
Tewfik BOUDIBA
PME Trainer
Stay efficient with EcoStruxurePower
Reply

Link copied. Please paste this link to share this article on your social media post.

MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant

Posted: ‎2020-01-31 01:50 AM

2 Likes
0
3029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-31 01:50 AM

TH110 or more generally "Thermal monitoring" and HeatTag are two different principles. TH110 is a battery free wireless temperature sensor for busbar or large cables. Installing and connecting to an upper system these sensors in various location of an MV or LV cubicle allow to follow in real time the temperatures of connections. This solution provide an accurate information of the real time temperature status of the equipment. it allow also to run algorithm corraleted with current measurement to detect abnormal heating. It can avoid infrared inspection.

 

HeatTag is a smart sensor analyzing the air in the cubicle, it detect particles released by insulation materials when reaching abnormal but not yet dangerous temperature. (it "smells" the heat).

 

The use of one or the other or a combination of both is the result of risk analysis and ratio benefit / cost analysis.

 

As a rule of thumb in switchboard with low load profile and/or limited number of busbar connections the risk of hot spot due to bad connection on busbar is low, the monitoring of cables connections of feeders with HeatTag only is a good compromise.

On the opposite in Switchboard with a heavy load profile or large switchboard with complex busbar arrangement with multiple busbar connections, monitoring the busbars connection with dedicated sensor is very relevant. HeatTag can then be used additionally to monitor feeders cable connection.

 

Mathieu Guillot

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore