Easergy T300 - Switchgear control failure code 6

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Easergy T300 - Switchgear control failure code 6
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
Romi
Romi
Cadet

Posted: ‎2022-10-03 12:26 AM . Last Modified: ‎2023-03-01 07:08 AM

0 Likes
3
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-03 12:26 AM . Last Modified: ‎2023-03-01 07:08 AM

Easergy T300 - Switchgear control failure code 6

I can't operate with my switch. Constantly receiving switch failure code 6. Tried switch manipulation in local mode (buttons) and remote mode (through web browser) but result is the same.

In manual I didn't find solution for my problem only the list of codes.

6 Command failed due to timeout waiting for enable from Head Unit
What is the reason for this problem? Where can I enable this?

Labels
  • Labels:
  • Medium Voltage
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TomBerry
Lieutenant JG TomBerry Lieutenant JG
Lieutenant JG

Posted: ‎2023-03-13 05:05 AM

1 Like
0
886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-13 05:05 AM

 

This code means that the SC has failed to get a response to its request to the Head Unit to check that the battery and power supply is in good condition and is available for the SC to use.

Normally the head unit will send its response (yes or no) within 5 seconds. If it doesn't send anything then there is a fault in the Head Unit (unlikely) or a problem with the configuration (more likely).

 

Please send a copy of your configuration, the event log and the system logs for the HU and SC to the support team for analysis. It may be that part of the configuration required for the switch control interlocks has been accidentally changed.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Rajasekar_Chandrasekar
Ensign Rajasekar_Chandrasekar Ensign
Ensign

Posted: ‎2023-03-14 03:19 AM

0 Likes
0
871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-14 03:19 AM

Hello,

 

could you please share the event log, System Log and configuration file

global-na-tech-support@schneider-electric.com

 

BR
Rajasekar

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
Lt. Commander

Posted: ‎2022-10-10 03:12 AM

0 Likes
0
1044
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-10 03:12 AM

@jean-luc_batard , could you please support to reply to this question about T300?. Thanks a lot for your help.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

TomBerry
Lieutenant JG TomBerry Lieutenant JG
Lieutenant JG

Posted: ‎2023-03-13 05:05 AM

1 Like
0
887
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-13 05:05 AM

 

This code means that the SC has failed to get a response to its request to the Head Unit to check that the battery and power supply is in good condition and is available for the SC to use.

Normally the head unit will send its response (yes or no) within 5 seconds. If it doesn't send anything then there is a fault in the Head Unit (unlikely) or a problem with the configuration (more likely).

 

Please send a copy of your configuration, the event log and the system logs for the HU and SC to the support team for analysis. It may be that part of the configuration required for the switch control interlocks has been accidentally changed.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Rajasekar_Chandrasekar
Ensign Rajasekar_Chandrasekar Ensign
Ensign

Posted: ‎2023-03-14 03:19 AM

0 Likes
0
872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-14 03:19 AM

Hello,

 

could you please share the event log, System Log and configuration file

global-na-tech-support@schneider-electric.com

 

BR
Rajasekar

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of