Earth Cable Size for TT system

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Earth Cable Size for TT system
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Related Products
product field
Schneider Electric
EcoStruxure™ Power Design – Ecodial

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2022-05-21 06:14 AM . Last Modified: ‎2024-11-22 04:25 AM

0 Likes
6
3631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-21 06:14 AM . Last Modified: ‎2024-11-22 04:25 AM

Earth Cable Size for TT system

I have used ecostructur power design to size my project. But earth size is half of phase conductor as usual. Why is it not used adiabatic equation for this and size PE accordingly. If so cable size will be very less. 

 

Please advise

 

Labels
  • Labels:
  • Power Distribution Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2022-05-25 03:49 AM

In response to Anonymous user
0 Likes
3
3564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-25 03:49 AM

Thanks for your comments.

 

As we are respecting the IEC 60364-5-52 and 5-54; We are ensuring the minimum permissible cross sectional area of the protective conductor, even with the following sub condition respected.

 

also respected.GIF

 

 

 

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2022-05-23 04:13 AM

0 Likes
5
3597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-23 04:13 AM

Hello,

 

Thanks for your query and interest on the 'EcoStruxure Power Design Ecodial application. 

 

Yes, there is an adiabatic equation for conductor sizing is available.

 

 

However, this can be applied during the following conditions only.

 

  • When calculating the ‘fault current capability/rating’ of the cable…It is generally assumed that the duration of the ‘fault current’ is short, and there is no heat is dissipated by the cable to the surrounding.
  • This is applicable only for the ‘disconnection time of the protection devices is not exceeding 5 seconds.

 

Limitations of adiabatic equation:

 

  • If the application of the formula produces ‘nonstandard sizes,’ then the conductors of the ‘nearest standard cross-sectional area shall be considered.’
  • It is necessary that cross sectional area; so calculated be compatible with the conditions imposed by the fault loop impedance.
  • The maximum permissible temperature of the joints should be taken in to account for the further decisions.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2022-05-23 10:05 AM

In response to Genghiz
0 Likes
4
3588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-23 10:05 AM

Hi,

 

Yes. but why is it exactly half size of conductor. If we calculate 3 ohm earth loop impedance(TT system) it will be very less value. 

 

Please advise. 

 

Can't they include it to the software ?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2022-05-25 03:49 AM

In response to Anonymous user
0 Likes
3
3565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-25 03:49 AM

Thanks for your comments.

 

As we are respecting the IEC 60364-5-52 and 5-54; We are ensuring the minimum permissible cross sectional area of the protective conductor, even with the following sub condition respected.

 

also respected.GIF

 

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2022-05-26 08:43 PM

In response to Genghiz
0 Likes
2
3538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-26 08:43 PM

Thanks. I am having earth loop impedance 3 ohm. Calculation gives me less than 2.5 mm2 for main earth cable size at main switch board. So if i use 4 mm2 cable will be satisfied right. 

 

Please advise. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2022-05-27 02:33 AM

In response to Anonymous user
0 Likes
1
3520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-27 02:33 AM

Actually phase size is 240 sqmm Cu/XLPE/PVC. Calculation says PE size very less for mentioned impedance. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2022-05-27 04:19 AM

In response to Anonymous user
0 Likes
0
3514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-27 04:19 AM

 

Thanks for your comments;

 

It would be better to discuss (over a call) with our support experts by sharing the screen and explaining the project scenario.

 

they would prefer to understand the "calculated fault level" and the complete network.

 

So, kindly raise a support case through the following link, and our representative would be able to reach you for the further analysis.

 

https://www.se.com/in/en/work/support/customer-care/contact-schneider-electric.jsp

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore