Does the ,CT/VT's which is located on busbar before the main circuit breaker, need to have covers on secondary connection points within the scope of 4b forming?

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Does the ,CT/VT's which is located on busbar before the main circuit breaker, need to have covers on secondary connection poi...
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
65
View All
Related Products
product field
Schneider Electric
Canalis Busbar Trunking System

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
Anonymous user
Not applicable

Posted: ‎2020-06-26 02:14 AM . Last Modified: ‎2021-10-28 01:15 AM

0 Likes
4
6130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-26 02:14 AM . Last Modified: ‎2021-10-28 01:15 AM

Does the ,CT/VT's which is located on busbar before the main circuit breaker, need to have covers on secondary connection points within the scope of 4b forming?

The question is described on title.Since every external circuit or voltage transformer producers do not send plastic covers for     S1-S2 connection points, we need to order them additionaly.

I would like to learn that  can the transformers be mounted on busbar without covers on connection points?

Labels
  • Labels:
  • Products
  • Tags:
  • 4b forming
  • breaker
  • busbar
  • circuit transformer
  • english
  • forming
  • iec
  • safety
  • voltage transformer
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
PascalL
Lt. Commander PascalL Lt. Commander
Lt. Commander

Posted: ‎2020-09-15 12:30 AM

1 Like
0
5950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-15 12:30 AM

The current transformer CT installed on busbars, links between main busbar and devices have no voltage on terminals. That the reason why their terminals are not insulated. To the voltage transformer or power transformer usually they are not installed into the form 4b, because it is not a standard installation the place is lacking. They are installed into an auxiliary area and in any case their terminals are insulated. 

Pascal Leprêtre.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-03-15 02:19 AM . Last Modified: ‎2021-03-15 02:25 AM

2 Likes
2
5552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-15 02:19 AM . Last Modified: ‎2021-03-15 02:25 AM

Hello CFK,

In my experience (for a panel builder), 4b-form is the highest form applicable. This means every component should be insulated and/or change-able when power is still on.

This also means connections with products are separated from the other products or sources.
I have a pdf image which may be useful in getting some insight into this, attached to this reply.

For my opinion; I would insulate as much as possible. You don't want any mass, particles or body parts able to touch anything that has power on it.

If I read the post before me correctly. If the parts were talking about is a component which doesn't have a current or source and you can't touch it and/or cant be touched by other materials falling in. Then its not necessary to do so.

Hope I was of any help.



 


Kind regards,

Rick

See Answer In Context

Attachments
  • Tags:
  • building form
  • english
  • panelbuilding
  • safety
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-03-15 03:40 AM . Last Modified: ‎2021-03-15 04:10 AM

In response to Anonymous user
0 Likes
0
5533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-15 03:40 AM . Last Modified: ‎2021-03-15 04:10 AM

''As much as I understand from 4b forming, all different functional units must be seperated from each other. ''

That is correct.

And in your case I would agree with your perspective and actions.
It would be the most logical thing to do so.


In the main line of thinking, we should look at where the buildings forms are for;

The building forms are made for protecting parts that are guiding or diverting currents to different locations, like a busbar or fuse. Protecting them from any human interaction or falling object.

Thats why this is the form that is most used when customers want to change or pull fuses without having to switch off power to work safely.

I think next to regarding the safety line of things there is also the common sence/practical use of doing so. I think it would be most logical to protect and/or cover such connections as much as possible.

In context; If we build a (standard) form-1 panel, we still cover alot or most of the copper rails from touch/objects even if the build form does not describe its necessity. Just a bit of service/common sense.


Kind regards,

Rick

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
PascalL
Lt. Commander PascalL Lt. Commander
Lt. Commander

Posted: ‎2020-09-15 12:30 AM

1 Like
0
5951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-15 12:30 AM

The current transformer CT installed on busbars, links between main busbar and devices have no voltage on terminals. That the reason why their terminals are not insulated. To the voltage transformer or power transformer usually they are not installed into the form 4b, because it is not a standard installation the place is lacking. They are installed into an auxiliary area and in any case their terminals are insulated. 

Pascal Leprêtre.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-03-15 02:19 AM . Last Modified: ‎2021-03-15 02:25 AM

2 Likes
2
5553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-15 02:19 AM . Last Modified: ‎2021-03-15 02:25 AM

Hello CFK,

In my experience (for a panel builder), 4b-form is the highest form applicable. This means every component should be insulated and/or change-able when power is still on.

This also means connections with products are separated from the other products or sources.
I have a pdf image which may be useful in getting some insight into this, attached to this reply.

For my opinion; I would insulate as much as possible. You don't want any mass, particles or body parts able to touch anything that has power on it.

If I read the post before me correctly. If the parts were talking about is a component which doesn't have a current or source and you can't touch it and/or cant be touched by other materials falling in. Then its not necessary to do so.

Hope I was of any help.



 


Kind regards,

Rick
Attachments
  • Tags:
  • building form
  • english
  • panelbuilding
  • safety
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-03-15 03:07 AM

In response to RHH
1 Like
1
5542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-15 03:07 AM

Hello, RHH-Eltechna;

Thank you very much for your kind interest and solution oriented perspective.

 

As much as I understand from 4b forming, all different functional units must be seperated from each other. 

 

In this case , you can imagine that there is live busbar (but of course in front of it there is cover to prevent any external touch),

and on that live busbar, we have current transformer.

 

Firstly, as you know current flows on current transformers secondary points.

 

Secondly, Busbars and current transformers are completely different functional units for me.

 

That's why , I think it should be covered.

 

Many thanks for the file that you shared.

 

Best Regards,

Cafercan Karsin

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-03-15 03:40 AM . Last Modified: ‎2021-03-15 04:10 AM

In response to Anonymous user
0 Likes
0
5534
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-15 03:40 AM . Last Modified: ‎2021-03-15 04:10 AM

''As much as I understand from 4b forming, all different functional units must be seperated from each other. ''

That is correct.

And in your case I would agree with your perspective and actions.
It would be the most logical thing to do so.


In the main line of thinking, we should look at where the buildings forms are for;

The building forms are made for protecting parts that are guiding or diverting currents to different locations, like a busbar or fuse. Protecting them from any human interaction or falling object.

Thats why this is the form that is most used when customers want to change or pull fuses without having to switch off power to work safely.

I think next to regarding the safety line of things there is also the common sence/practical use of doing so. I think it would be most logical to protect and/or cover such connections as much as possible.

In context; If we build a (standard) form-1 panel, we still cover alot or most of the copper rails from touch/objects even if the build form does not describe its necessity. Just a bit of service/common sense.


Kind regards,

Rick
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of